I'm looking to rewire the power switch for my boiler as I want to move the wires to clean up the overhead in the basement. While I'm at it I'm considering adding a second switch next to the burner wired in series w/the one at the top of the basement stairs. That is, BOTH switches would need to be on for the boiler to run. This way when one is working on the boiler the switch is "right there" and you can see it's off. Anyone see a problem with this idea?

Also going to put a GFI outlet before the switch at the boiler so the worker has ready-access to power. Make sense?
 

·
Master General ReEngineer
Joined
·
9,768 Posts
Ayuh,... I'm glad that's all code friendly,...

I've wired my 2 houses that way...
Hope the Gfi part ain't "Needed", as mine are just standard outlets....
I did use the purty Red switch plates for the switches though....
 

·
Super Moderator
Joined
·
20,894 Posts
Ayuh,... I'm glad that's all code friendly,...

I've wired my 2 houses that way...
Hope the Gfi part ain't "Needed", as mine are just standard outlets....
I did use the purty Red switch plates for the switches though....
If the the room where the receptacle is located is unfinished then GFCI is required.
 

·
Registered
Joined
·
349 Posts
Discussion Starter #6
Don't tap the boiler circuit for an outlet, that's a code violation.
That's what I was unsure of, even if the outlet is for the boiler service? Code reference by any chance? I'm on NEC 2011... Yes, I know it's only the 4th day of 2011, my AHJ is one of those "current version" AHJs.
 

·
Registered
Joined
·
367 Posts
That's what I was unsure of, even if the outlet is for the boiler service? Code reference by any chance?
It's been a code requirement for a long time.

422.12 requires central heating equipment to be on an individual branch circuit. Exceptions being pumps, humidifiers, etc that are associated with the equipment.
 

·
Just call me Andrew
Joined
·
2,279 Posts
I'm looking to rewire the power switch for my boiler as I want to move the wires to clean up the overhead in the basement. While I'm at it I'm considering adding a second switch next to the burner wired in series w/the one at the top of the basement stairs. That is, BOTH switches would need to be on for the boiler to run. This way when one is working on the boiler the switch is "right there" and you can see it's off. Anyone see a problem with this idea?

Also going to put a GFI outlet before the switch at the boiler so the worker has ready-access to power. Make sense?
Aside from the outlet, I just did this as well, both switches in series. The local electrical supplier had the nice red switchplate covers. Both a 4x4 one for downstairs and a standard switch cover for the one upstairs.
 

·
Registered
Joined
·
349 Posts
Discussion Starter #9
It's been a code requirement for a long time.
Wasn't doubting the reference, just want to read it for myself. Appreciate it.

Guess I'll run the receptacle off a different circuit. No worries there, I've got several I can chose from. :)
 