I need to free up a slot on my panel. It is full and will not take half sized breakers. Fortunately my breakers are UL approved to take two wires, so it is code acceptable to run two circuits to them.
I have many circuits that are way underutilized, but the two that seem cleanest to me are two 15a circuits.
The first has 6 recessed lights on it. With them all on, I measure 3.15a.
The second has a ceiling fan, an exhaust fan, and two ceiling lights. With everything going I measure 2.8a. That seemed low to me, but I looked it up and both fans are less than an amp each.
Nothing could be added to either circuit.
So, unless I am just missing something, running both circuits to the same breaker will have a maximum of 5.9a at the breaker. It seems fine to me. Any issues?
Second question: the bulbs in the first circuit are PAR30, 75w, 130v, all on dimmers. I would expect to see about 3.5a.
I am thinking that even full on, perhaps the dimmers reduce the current a bit, or maybe 130v bulbs draw less current at 120v than might be expected.
What do you think?
I have many circuits that are way underutilized, but the two that seem cleanest to me are two 15a circuits.
The first has 6 recessed lights on it. With them all on, I measure 3.15a.
The second has a ceiling fan, an exhaust fan, and two ceiling lights. With everything going I measure 2.8a. That seemed low to me, but I looked it up and both fans are less than an amp each.
Nothing could be added to either circuit.
So, unless I am just missing something, running both circuits to the same breaker will have a maximum of 5.9a at the breaker. It seems fine to me. Any issues?
Second question: the bulbs in the first circuit are PAR30, 75w, 130v, all on dimmers. I would expect to see about 3.5a.
I am thinking that even full on, perhaps the dimmers reduce the current a bit, or maybe 130v bulbs draw less current at 120v than might be expected.
What do you think?