The first rule of off-grid life is "cheap, stupid, successful: pick two".
I see a disturbing number of off-grid projects fail, and the reason is real simple: they thought they could have all three. Not surprisingly (thanks to Dunning-Kruger), these people DO NOT scrupulously identify their failures and iterate on their mistakes; they just get frustrated and huck the whole thing and pay for the utility service drop.
So with that said, the cabin (more like a small house) will have a mini-split for AC and heating. Due to the size (16X24) I require an 18K BTU unit to adequately heat and cool.
(Before anyone asks about the AC size. It was sized by the AC manufacturer as the building is lofted with 22ft ceilings. We thought about 2 110V units but that increased cost and complexity.)
The problem is your presumption (16x24
therefore 18K BTU) does not work. You can't derive that from that.
The figures you're relying on there are just stock A/C salesman drivel... they want to sell an A/C unit and they don't have any data, so they take blind wild guesses on the basis of "err on the high side". And who cares since it's grid-powered. It's not like somebody has to rack additional batteries or buy a bigger generator LOL.
What you really need is good data on
- The shade, which reveals the primary enemy of your A/C unit: Solar Gain. Solar gain is about 100W (341 BTU/hr) per square foot (square on with the sun, that is). Solar panels or other shader devices, if they have airflow behind them, can greatly decrease the solar gain felt by the building.
- The insulation of the building, which varies dramatically and has a huge impact on HVAC needed. A tight modern building can run its A/C from midnight to 7am and hold its cool literally all day. My drafty old cottage, no way no how! This matters.
- The local climate, obviously. Seattle is a different deal than Phoenix.
Then you can size the unit properly. Size matters when you're off grid.
Of course all mini-split over 12K BTU are 240V (I bet you can see where this is going). Since all my current power options are 120V I want to use a transformer to run the mini-split. Here is where my knowledge lacks.
All your current power options are 120V because you are cheap, and chose to minimize the size of your system. That's fine and good, but then -- you must sacrifice "stupid" OR "successful". You can guess my recommendation LOL.
Now, when you see a 240V unit, that is a strong signal from the manufacturer that the unit requires too much power to be practicably powered from 120V. So watch out. We'd need the nameplate specs and I don't see where you've shared them.
I would like to use a standard transformer (like an ST-5000) to step the voltage up to 240 to run the AC.
That's not a "standard" transformer at all. That's a
cheap Chinese transformer - typical, unsafe, illegal rubbish sold
direct mail only to slip it by the FTC and other regulators. (Customs is simply too busy to intercept them, but they would if they could). Of course all the junk stores - wish.com, eBay, AliExpress and Amazon Marketplace are just glutted with them, to the point where you can't find a real one on those crap marketplaces. Also the low price twists your mind so you are unwilling to pay for a real one.
If you didn't know, Amazon opened their sales website to 3rd party sellers, so effectively it's eBay now.
Here's the problem. An HVAC listed for sale in the US is expecting 240V, yes, except
each leg is only 120V from ground. The unit may not be built, tested or approved or 240V phase-ground voltages. On the other hand if it's also sold in Europe, it would be, since their power is 240V hot-neutral. (and a whopping 416V between 2 phases of hot - distribution is 3 phases, not necessarily to every home.)
And then NEC has rules relating to allowed voltage vs neutral - some rules prohibit >150V to neutral. It's unfortunate that you committed to 120V, since all this is easy with split-phase generators and inverters. But this is a typical problem as you grow an off-grid system - maybe it's time to admit you outgrew your initial build. That's hardly failure.
But here's another problem with some units: they run 240V compressors but have 120V head units. That means they need genuine neutral. Now you could synthesize that with a buck-boost transformer, by configuring it to "boost" on the opposite side of neutral, thus synthesizing a "-120V"*. That would also be safer. But those are not $169 for 5KW. (on the other hand they don't have to be so large, since only half the power goes through them).
* Of course it's AC power, so +120V and -120V aren't really valid, or to be more precise, not valid
half the time lol).
In case someone down the road reads this and want to understand the math. The unit I bought has a COP of 3.0.
Yeah, but it's not like that's its COP end of story. That's its COP
in certain test conditions. Above those, COP will be better; below it worse. For instance, add freezing rain and it's having to do a lot more defrost cycles and the COP suffers as a result.
But it certainly is not a Honda and I don't care what any db test shows they are not as quiet.
Because they're measured in cheap Chinese decibels LOL.