The proper way to test it is to use a differential pressure manometer and tee it into the hoses for the pressure switch. You need to know the "WC rating of the switch also. Hopefully it is written on the label of it.
Your inducer fan may be just barely producing enough vacuum/draft to close the pressure switch. Playing with the hoses bumps it and sometimes it works. The inducer may be worn or not turning fast enough or you got some blockage in the heat exchanger.
Point is w/o checking the pressure on the switch you will never know. This is some advanced tech troubleshooting so if you are not comfy with it then call a Pro.
Amazon has cheaper meters but I am not sure they are accurate as you get what you pay for and at this price point it is Chineez stuff.
Pros use more expensive UEI and Fieldpiece meters but they are in the hundreds of $$.