I believe this model has both high and low pressure switches to monitor system refrigerant pressures. Often they are just wired in series with the Y input that activates the contactor, although some manufacturers employ a "3 strikes and your out lockout" by having these switches monitored by the defrost control's micro.
So yes in your case the high pressure switch could open while the unit is running, but as soon as the pressures drop below the switch setpoint and the tstat is still calling for unit to run it will run again until it trips again....cycling on the pressure switch.