Hi there,
12 year old Trane natural gas furnace, Model UD100R9V5J
Furnace sequences through:
1. Draft blower comes up to speed
2. 1st stage pressure switch closes
3. Igniter comes on for 10+ seconds
4. No gas to burners
5. Igniter goes off
6. Sequence repeats
Observations: Flashing LED on circuit board shows flashing slow then flashing fast (calling for heat). I haven't observed any other error flash codes.
I disconnected the leads to the gas valve and ran through the startup sequence above. Used multi-meter and found no 24V DC between the common and Low Fire.
Bad board??
Thanks in advance..