FHA loans require a mini home inspection done by an appraiser. Appraiser said that THNN wires located in the attic needed to be in conduit.

Home inspector says it is okay since the wires are more than 6 feet from attic access and something about protected from damage since they are not laying on the truss.

My handyman says that all wire has to be in conduit unless it is NM while another contractor says that its okay w/ GFCI protected, its safe.

I am convinced that the NEC says it needs to be in conduit. How did other people cite specific examples of when it does not need to be? Does the NEC say different things?
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
Home inspector says it is okay since the wires are more than 6 feet from attic access and something about protected from damage since they are not laying on the truss.
:laughing: :laughing: :laughing: :laughing: :laughing: :laughing: :laughing: :laughing: :laughing: :laughing:

What a MORON!
 

·
Banned
Joined
·
17,248 Posts
Get a HI that knows the code...when an appraiser knows more :whistling2:
Don't hire anyone that thinks putting a GFCI on it solves the problem

Inside an HVAC cabinet conduit not needed
Running to the cabinet conduit is needed
I do not know of any code that allows loose THHN
 

·
Super Moderator
Joined
·
22,753 Posts
:laughing: :laughing: :laughing: :laughing: :laughing: :laughing: :laughing: :laughing: :laughing:

What a MORON!
Totally agree. Demand a refund and get someone who knows what they are doing. If he thinks that is good what else did approve as good, rubber hose used for plumbing inside the house.:whistling2:
 

·
" Euro " electrician
Joined
·
5,369 Posts
FHA loans require a mini home inspection done by an appraiser. Appraiser said that THNN wires located in the attic needed to be in conduit.
Well., the THHN conductors must be in conduit no question asked.

Home inspector says it is okay since the wires are more than 6 feet from attic access and something about protected from damage since they are not laying on the truss.
If NM it is not a issue but any cable less than 2 meters( 6 Feet ) from scuttle hole it have to be properly secured. The conduit is not a issue as long it properly routed and secured.

My handyman says that all wire has to be in conduit unless it is NM while another contractor says that its okay w/ GFCI protected, its safe.
I am suprised that your handyman nail this one and how the world did that contractor say it is ok with RCD { GFCI } protection espcally with exposed THHN/ THWN conductors I don't buy that story someone is not really understand the code very clear on this matter.

I am convinced that the NEC says it needs to be in conduit. How did other people cite specific examples of when it does not need to be? Does the NEC say different things?
Any THHN / TWHN or other type of conductors { cable have limited coverage on this part } It must be in conduit no question asked it is allready written in the NEC code no if or but or Conneries .,,

The only time it don't need the conduit if part of equiment.

Merci.
Marc
 