Njuneer
Joined
·
954 Posts
Discussion Starter #1
Just spotted a safety issue at someone's home and I would like to get it corrected before something happens. This will be a temporary deal and will be removed in approx a year.

Basically an attached garage has a proper welder 50A circuit run from the main breaker to the garage with proper receptacle. Then there is a 3ft adapter made to plug into the 50A receptacle, and other end has a 20A/240V receptacle on it that plugs into a long 12ga cord that is running a pump.

So anything that is 12ga or even the plugs, are not safe.

My first thought was just to go install a 20A breaker and all is well, and switch it back later, but thought I might see if there are other simple solutions? I have a small 50A load center I could stick a break in, but...... Thought I would check.
 

·
Super Moderator
Joined
·
21,785 Posts
One year is not temporary.
If the welder circuit has a neutral the best solution is to replace it with a small breaker panel.
 