I have Goodman 3 ton I just installed about a month ago. Have been running for a couple of days now the outside temp on the big line is 45 F out side and 47 F air coming out of the vent is this a good temp ?????????? 
Your condensing unit is a 3 ton Goodman, your compressor inside of the Goodman is a Copeland.. My compressor is a Goodman CKL36-1D it's a 3 ton 10 SEER R-22 unit used . Bryant 394D-0036100 :thumbup:
if your indoor temp out of a register is 47 then the temp going back to the furnace should be around 70 to 75. measureing the out door line temp doesnt help if you dont know the pressure of the line
I just called my wife and had her check difference between the 2 , it's 20 f difference. I asked them guys at alpine air about that txv valve they said that I didn't need one that the orifice would work better , and so i believed them because that part was around 100. 00 vs the 10.00 I spent on the orifice . I even called them a second time and talked to someone else they told me the same thing, I remember him saying something about 80 psi is where it was a at and then he was done.
Not really, as this would defy physics.That will not happen with a txv, ever, unless it goes bad. The system efficiency (coil capacity which equates to air temperature) stays the same regarldess of ambient temperatures.
Coil capacity stays the same is what I meant.
nope, we just went over it class for the past three months so it's studied.You should get Modern Refrigeration and Air Conditioning. And read and study it. Then you'll see the flaw in that statement also.
The explain how the coil can be at the same capacity with an entering air temp of 70°F at 50%RH at a coil temp of 45°F, as a coil at 40°F, both with 12°F SH. They can't and aren't. Either you misunderstood, or your teacher/instructor is wrong.nope, we just went over it class for the past three months so it's studied.
The only way the temperature of the coil would defer would be by way of capacity, amount of refrigerant in the coil, so with a txv that refrigerant level would be maintained, correct?The explain how the coil can be at the same capacity with an entering air temp of 70°F at 50%RH at a coil temp of 45°F, as a coil at 40°F, both with 12°F SH. They can't and aren't. Either you misunderstood, or your teacher/instructor is wrong.