I added a wire to an existing connection in the attic in order to mount a light fixture in our dining room.
When the switch is turned on, the volt meter reads 120 volts between the black/white wires in the ceililng mount box.
When the switch is turned off, the voltmeter reads 25 volts between the black/white wires in the ceiling mount box.
Any ideas for the 25 volt reading on the voltmeter when the switch is in the off position? Would it be okay to mount and hook up the light fixture with the 25 volt reading?
Here is a picture for the connection.
http://i51.tinypic.com/2d122xj.jpg
Thanks for your help,
Tom
" Euro " electrician
The other thing is you denfienly need a junction box on this one as soon I hit the link and I can see where this is going and you have a switch loop allready
Do you want the ceiling fan to be unswitched { use the pull chain for the fan control } ? and the new luminaire to be switched controlled then you have to resort it and get it correct otherwise if you hook them up wrong you can trip the breaker or pop the fuse out.
Merci,
Marc
Does the switch turn the light on and off? If the switch is correctly operating the light, don't worry about it; it's phantom voltage.
BTW: why is there a single Black wire connected to a group of Whites?
Hi Sirsparksalot,
I hooked the light fixture up today and it works fine using the light switch. I won't worry about the phantom voltage as you say.
The black wire connected to the group of whites goes to the light fixture.
The white wire going to the light fixture is connected to the white wire on the switch wire. Is this connected correctly?
Thanks,
Tom
Merci,
Marc
Hi Marc,
A junction box would most definitely be beneficial as you suggest. I don't know what a switch loop is.
Yes, I want the ceiling fan to be unswitched as we can use the pull chain to control it. The ceiling fan is hot and work fine now. The luminaire now works properly with the light switch.
Thanks,
Tom
Super Moderator
There is a bunch of thing wrong with this setup.
As it is wired now the shell of the light socket is hot. If you were to unscrew a bulb with the power on the exposed threaded portion would be live.
The white wire to the light should go to the bunch of whites.
The black wire the light should go to the black wire from the switch.
The white wire from the switch should go the bunch of black wires.
You must have a junction box. This is called a flying splice and is not permitted by code.
1 - 6 of 6 Posts