I am about to wire up my switch for a new outdoor patio light, and want to ensure my plan is good... Have three sets of UF 14-2 to connect:

1) Goes to light
2) Comes from outlet and provides power
3) Goes to a second outlet in this circuit

My plan was to pigtail all the power lines, neutrals and grounds... Then run 1 power to power on switch, one neutral to the switch and one ground to the switch... Any issues with doing it this way???

Thanks much and TIA...

vr
Roger V
 

Attachments

· Registered
Joined
·
628 Posts
Cut out all but about a 1/4" of insulation on the wires coming into the box. I see that you have a nick in the neutral of the conductor on the right hand side.

You will splice the (2) black wires together that are line and feeder to the other device and pigtail one other to the line side of the switch. The black from the light to the load side of the switch. All others are spliced together respectively.

I do not see anything to secure the conductors in the box. I never use plastic boxes, I really hate them. I also never use romex. I also never, ever cross power and lighting on the same circuit. But that is beside the point. Some folks like things a little different. But if you have ever had to work in the dark on an outlet, or without power while working on a light, you will do as I do from that point forward. I also twist all my splices, and tape the wire nuts so that no dust can get into the connection. I tape the device to cover the screw as well. A little extra time now, goes a long way in the future.
 

· Registered
Joined
·
53 Posts
Discussion Starter · #4 ·
connect all neutrals together,


connect all grounds together, and a pigtail ground from there to the switch,


connect blacks #2 and #3 together, with a pigtail black from there to the switch


connect black of #1 to the switch
Cut out all but about a 1/4" of insulation on the wires coming into the box. I see that you have a nick in the neutral of the conductor on the right hand side.

You will splice the (2) black wires together that are line and feeder to the other device and pigtail one other to the line side of the switch. The black from the light to the load side of the switch. All others are spliced together respectively.

I do not see anything to secure the conductors in the box. I never use plastic boxes, I really hate them. I also never use romex. I also never, ever cross power and lighting on the same circuit. But that is beside the point. Some folks like things a little different. But if you have ever had to work in the dark on an outlet, or without power while working on a light, you will do as I do from that point forward. I also twist all my splices, and tape the wire nuts so that no dust can get into the connection. I tape the device to cover the screw as well. A little extra time now, goes a long way in the future.
Boy, glad I asked... Would've screwed that up big time... What would I use to secure the conductors in the box???

Thanks again,

Roger V
 

· Registered
Joined
·
53 Posts
Discussion Starter · #7 ·

Attachments

· A "Handy Husband"
Joined
·
15,054 Posts
The switch you show is a 3 way, not needed, you need a single pole switch. A neutral is never switched in normal wiring configurations.
 

· Registered
Joined
·
8,194 Posts
Boy, glad I asked... Would've screwed that up big time...
Part of the problem is that cables (bundles of wires inside a sheath) are color-coded for the convenience of the cable manufacturer, not to indicate purpose/function. I strongly recommend (and for novices, *very* strongly recommend) you pause to understand wire function, and then, use colored electrical tape to re-mark the wires by their function.

- White for neutral (mandatory)
- Black for always-hot
- Red for switched-hot
- Blue for 2nd switched-hot in the same box
- Yellow for both 3-way travelers (no need to tell them apart, but 2 yellows is very distinctive and not likely to be mistaken for anything else).
- Blue for 2nd set of 3-way travelers if that ever comes up

Always mark both ends of the wire (at the same time so you don't forget).

So, since you want the lamp controllable by a switch and not on 24x7, the lamp's hot is a switched-hot, that gets red.

From there it's downhill: Plain switches get red and black (they connect always-hot to switched-hot, or they don't). They don't have any use for neutral (but smart switches do).

Once you have retagged all your wires by function, just join like color to like color. Easy peasy!


What would I use to secure the conductors in the box???
Wire nut. Do it properly - crank it down HARD and do a "pull test" holding the nut in one hand and yanking each wire in turn with the other. If any pull out, you bodged the job, refine your method and redo. Never, ever reach for tape as a "crutch" to hold a shoddy wire-nut job together: if they're falling apart they are also a bad connection, and that will cause an arc-fault and a fire. If a wire-nut is fighting you a lot, make sure the size is appropriate for the job. Yellow is great for 2 wires, but for 3+ consider red nuts.

You can also use Wago style lever-nuts, Alumiconn lug connectors (if you use them on all copper wires, I won't tell ;) ) or for 4-8 wires, the big daddy, MAC Blocks.

They also make stick-the-wire-in-the-hole (and it grabs) connectors, but they have the same problems as "backstab" connections on switches/receps.

In some cases you can use the recep or switch itself as a splice block - look for "screw-and-clamp" style receps/switches that take 2 wires under each screw. Those are the easiest to work with and provide good connection. But using the device as a splice can confuse novices.
 

· Super Moderator
Joined
·
18,311 Posts
The push in connectors mentioned above do not have the same construction or problems as the backstabs on a device. They are much more robust. This can clearly be seen through the plastic shell.
 

· A "Handy Husband"
Joined
·
15,054 Posts
:confused1:




the switch i see appears to be a single pole, not 3 way,


the screw on the other side is a ground screw.....or so it appears to me anyway
I looked again. The single screws looked black when I first looked, it now looks green. Yes a single pole.

Sent from my RCT6A03W13E using Tapatalk
 