Hello,
I have wall oven that has ceased to function some time ago. After multiple service tech visits, today they determined that the issue is my house wiring, which I don't completely believe yet and am looking for the thoughts of others.
The tech pulled the oven today, disconnected the wire whip from the terminal blocks and then we measured the voltages at the wire whip:
L1-Ground = 120V
L2-Ground = 120V
L1-L2 = 240V
Perfect, just as it should be right?
He reconnects them to the oven terminal block and now we have new voltages:
L1-Ground = 240V
L2-Ground = 0V
L1-L2 = 240V
The tech called in to some tech support line and explained it all -- their answer is that those voltages measured at the whip without the oven connected are invalid because there's no load attached to it and thus the ground can be floating. Thus, their conclusion is that the oven is fine and it's the house wiring that is faulty (nevermind the fact it worked for 10 months with this oven and 13 years with the previous oven).
While I agree that the DMM doesn't represent much of a load, my hypothesis is that somewhere in the oven, L2 is shorted to ground and that's why we're getting the readings above.
I'd welcome any thoughts anyone has on this, as well as any tips on isolating my suspected short (I guess just resistance test every connection on L2 to the metal cage?).
Thanks!
I have wall oven that has ceased to function some time ago. After multiple service tech visits, today they determined that the issue is my house wiring, which I don't completely believe yet and am looking for the thoughts of others.
The tech pulled the oven today, disconnected the wire whip from the terminal blocks and then we measured the voltages at the wire whip:
L1-Ground = 120V
L2-Ground = 120V
L1-L2 = 240V
Perfect, just as it should be right?
He reconnects them to the oven terminal block and now we have new voltages:
L1-Ground = 240V
L2-Ground = 0V
L1-L2 = 240V
The tech called in to some tech support line and explained it all -- their answer is that those voltages measured at the whip without the oven connected are invalid because there's no load attached to it and thus the ground can be floating. Thus, their conclusion is that the oven is fine and it's the house wiring that is faulty (nevermind the fact it worked for 10 months with this oven and 13 years with the previous oven).
While I agree that the DMM doesn't represent much of a load, my hypothesis is that somewhere in the oven, L2 is shorted to ground and that's why we're getting the readings above.
I'd welcome any thoughts anyone has on this, as well as any tips on isolating my suspected short (I guess just resistance test every connection on L2 to the metal cage?).
Thanks!