If you separate the neutrals from the grounds what happens if
the bare ground wire touches the back of the panel?
Or is the neutral bar that you remove the bonding screw from
to separate from the panel?
 

·
Engineer
Joined
·
191 Posts
If you separate the neutrals from the grounds what happens if
the bare ground wire touches the back of the panel?
Or is the neutral bar that you remove the bonding screw from
to separate from the panel?
The back of the panel will be tied to the ground (so entire cabinet is grounded.) The neutral bar is what is completely isolated from ground in a sub.
 

·
Registered
Joined
·
264 Posts
Discussion Starter · #4 ·
Are you asking how to size the;

Equipment Grounding Conductor? 250.122

Grounding Electrode Conductor? 250.66

Grounded Conductor (the neutral) 220.61
In what way is the "neutral" considered a grounded conductor?
 

·
Licensed Electrician
Joined
·
4,352 Posts
Are you answering your own questions?
 

·
Super Moderator
Joined
·
16,920 Posts
I think they are looking to see if they would be using the correct article to size the conductors. They seem to have found an answer, but want someone to say whether it is correct.
 