I live in NJ in a town that follows NEC 2005 codes. I live in a ~1800square ft. house with 1 primary electric panel. Looking for planning help to prep for design and permit application.

I'm looking to install a new sub-panel (Square D QO 100A / 20 slots / with 100A main breaker) very close to the main panel and feeding it with a 100A breaker. Does feeding 100A to the sub-panel from a main panel that is only 100A cause any code violations?

I'm looking to move a 10-12 breakers off the main to the sub and then add in a breaker to feed in a generator using an interlock kit.

I've researched other items and plan on unbonding / keeping separate neutral from ground in the sub panel. Also using #3 THHN copper with #8 ground through PVC conduit between main and new sub-panel.

Any tips and help greatly appreciated!!
 

·
Licensed Electrician
Joined
·
4,352 Posts
All a sub panel does is increase the available spaces to install breakers. If you have a full 100A panel, I suspect you will need to upgrade the service to 200A, and then install the sub panel if still needed.

To start, you could list all 240V appliances...Water Heater, Dryer, Furnace, AC, Range, Hot Tub....
 

·
NJ DIY'er
Joined
·
2 Posts
Discussion Starter #3
The only 240v items are:

- Dryer
- AC

If I didn't upgrade to 200A and kept it at 100A, would I be violating any codes? I am hoping I don't need to upgrade my main to 200A.
 

·
Super Moderator
Joined
·
9,093 Posts
You do not need a main breaker in the sub, unless you already have the panel.

A 60 amp feed should be more than enough.
 

·
" Euro " electrician
Joined
·
5,369 Posts
You should be ok with the load as you posted there.

60 amp subpanel is plenty big for that useage.

Merci,
Marc
 

·
Registered
Joined
·
132 Posts
all a sub panel does is increase the available spaces to install breakers. If you have a full 100a panel, i suspect you will need to upgrade the service to 200a, and then install the sub panel if still needed.

To start, you could list all 240v appliances...water heater, dryer, furnace, ac, range, hot tub....

i very well agree...
 

·
Lic Electrical Inspector
Joined
·
1,843 Posts
I live in NJ in a town that follows NEC 2005 codes. I live in a ~1800square ft. house with 1 primary electric panel. Looking for planning help to prep for design and permit application.

I'm looking to install a new sub-panel (Square D QO 100A / 20 slots / with 100A main breaker) very close to the main panel and feeding it with a 100A breaker. Does feeding 100A to the sub-panel from a main panel that is only 100A cause any code violations?

I'm looking to move a 10-12 breakers off the main to the sub and then add in a breaker to feed in a generator using an interlock kit.

I've researched other items and plan on unbonding / keeping separate neutral from ground in the sub panel. Also using #3 THHN copper with #8 ground through PVC conduit between main and new sub-panel.

Any tips and help greatly appreciated!!
No town in New Jersey is following the 2005 NEC. AS of 11/7/12 the 2011 NEC has been adopted with ammendments. Follow the links in my signature for DIY in New Jersey.
 