so need help on setting up a 24 outlet room that needs to be able to hold anywhere from 600 watts to 1000 watts and at least 24 units. can i run this off a 100 amp main panel. to a sub panel then to a outlet board.
thanks for any help
Electrician
So each of the 24 plugs will be pulling 600W to 1000W, if so you are going to max out your 100A main pretty quickly(1000x24/240=100A). This is not takeing into consideration any thing else that is on the 100A service.
There is a big difference between 600 & 1000 watts. 30 systems @ 600 watts each or 18 @ 1000 watts each would put you at a 75% load. Is there lighting or anything else going to be run off the sub? What size service is going to be feeding this sub? You need to do a load calc to see if you main service can support the additional load.
edit: oops, missed that you said you main is 100A. A 100A main isn't going to cut it unless this is the only room in the place and has no A/C or appliances.
Chance are that if you house is on a 100A main, you don't have much extra capacity. You need to provide much more detail about exactly what the draw is of the rest of the house. Central A/C? Refrigerator? Hot water heater?, ect. You are going to need to upgrade you electrical service and/or main panel to run 24 PCs. All those computers are going to generate a lot of heat that will need to be controlled.
Electrician
You'll also need power factor correction.
http://www.youtube.com/watch?v=AI_e3dF14eg
Very true but your power company probably charges you per watt(actually KW) so power factor does not effect your bill. He is one of those guys who probably say that by fixing your PF you will lower your electric bill, if you are billed by the watt your watts will never change even if you go from a .1 power factor to a .99 power factor.
This comes into effect if you are a commercial or industrial customer where you do get charged for your apparent power.
Banned
Is this a PC room or a Data center (servers) ?
Pc's use at most (usually) around 300 watts each Max
Much less on average when running
LCD screens use less then 100w - down to about 35w on a 17" model
Where are you getting 600-1000 watts for a PC?
Wire Chewer
I am guessing he took 600 from the power supply "Rating". This does not mean it will actually be drawing 600 watts. A PC will draw a few hundred watts normally, maybe more if it's a powerhouse gaming machine like triple SLI with 8 hard drives and a squirrel cage fan or something.
1 - 15 of 15 Posts