DIY Home Improvement Forum banner

1 - 8 of 8 Posts

·
Registered
Joined
·
2 Posts
Discussion Starter · #1 ·
Is it a good pratice to install Styrofoam Insulation sheets over the wood sheathing (to form a thermal break) and then put fiberglass insulation on the inside between the 2 x 6 studs?
 

·
Registered
Joined
·
37,305 Posts
No because you would be installing a vaper barrier on the wrong side of the wall.
The vaper barrier needs to be on the inside.
 

·
Registered User
Joined
·
11,730 Posts

·
Registered
Joined
·
37,305 Posts
Pleas go back and add your location to your profile for ansewers not questions.
Just go to the top left and tap on your name where it says welcome to make the change.
 

·
journeyman carpenter
Joined
·
3,480 Posts
in a cold location its perfectly fine depending on the type of foam your using as open cell foam has to have house wrap installed over it. .closed cell foam can just be put on hte wall by itself but be sure to use shiplap foam and tape the vertical seams horizontal seams are left open so it can still breathe
 

·
Roofmaster
Joined
·
3,731 Posts
As long as the poster knows Blue Styrofoam (EXPS) by Dow Chemical from bead board (EPS) The White Cheap Stuff.

Styrofoam is Blue, and is a Registered Trademark of Dow Chemical Co. It is a closed cell extruded polystyrene insulation. It is so resistant to water that it is used in inverted configuration in low slope roof systems where it is placed on top of the roof membrane. (Protected Membrane Roof System).

And Yes, we need to know where you are to know where the Vapor Barrier/ Retarder should go, but Generally Speaking you want the dew point to fall in about the middle of the insulation package.
 

·
Registered
Joined
·
2 Posts
Discussion Starter · #7 ·
Thanks for your reply regarding the styrofoam insulation over the OBS, I am having a new home built in Nova Scotia (framing in-process) and was wondering if it may prevent the vapor from excaping.
 

·
Registered User
Joined
·
11,730 Posts
Exterior foamboard is fine anywhere, warm or cold location. It should be thick enough to keep the backside of the sheathing warm so moisture doesn't condense there or on the cavity insulation (dew point= first condensing surface); http://www.buildingscience.com/docu...ld-weather-condensation-using-insulation/view

http://www.buildingscience.com/documents/insights/bsi-049-confusion-about-diffusion

The open-cell foam (EPS- more than one type) is fine for side-wall applications (hard to get the R-value/window detail with thickness for your location), even below grade; http://archive.nrc-cnrc.gc.ca/eng/ibp/irc/ctus/ctus-n36.html

The best place for the WRB (housewrap) is between the foam/structural sheathing, whether cc or oc; http://www2.dupont.com/Tyvek_Weathe...ith_Exterior_Foam_Sheathing_Tech_Bulletin.pdf

http://www.buildingscience.com/documents/published-articles/pa-foam-shrinks

Describe the wall make-up.

Gary
 
1 - 8 of 8 Posts