Is it okay to put multiple ground wires in one hole in the ground block and multiple neutral wires in one hole in the neutral block in the main panel?
May be possible for the ground wires, but not possible for the neutral wiresIs it okay to put multiple ground wires in one hole in the ground block and multiple neutral wires in one hole in the neutral block in the main panel?
No it's not!most competent electricians will frown upon doing this.....however, its fine
Code doesn't allow two neutrals under one screw.Why isn't it fine?
Some panels (especially older ones) have a limited number of neutral/ground bar slots. Doubling ground wires is compliant, doubling neutrals is not.What would be the reason to have two under a single nut? Usually there’s sufficient space for each neutral to have its own terminal. If you can’t reach an open one just pigtail another wire to reach an open spot.
Sent from my iPhone using Tapatalk
Why isn't it fine?
It violates both the UL listing and the NEC.trust me....its done all the time,
Aha! This is why I posed the question in the first place, to find out if an electrical problem could be created by it. So, it's not that having multiple neutrals in one hole is the problem (because the electricity is all lumped together on the neutral bar), but that causing a disconnect (voltage surge?) in one of the other circuits in the same hole, especially if the juice is still on while loosening the set screw. I hope I got that right...You can add a additional ground bar to make more room but the easiest way is to take several ground wires and wire nut them to a pigtail and use a single space on the bar. You can use any color wire nut. The pig tail must be the size of the largest ground wire. You can't do this with neutrals.
BTW, the reason you cannot have 2 neutrals in one slot is that if you open a neutral inadvertantly, you can cause issues with the other circuit. If you do this with a MWBC, you will fry electronics.
Sent from my Moto E (4) Plus using Tapatalk
Awesome! I reckon stuff like this is why there's an Electrical Code. Even if it looks like it makes sense to do something a certain way, it may not be correct/safe.Multiple neutrals on one terminal in a breaker box is against code and dangerous - even life threatening. I am astounded that anyone here would condone the practice, even if they have seen it done. The reason:
Say you are working on a circuit and have opened the breaker to ensure the circuit is safe to work on. However, the neutral of this circuit is doubled with that of another - still hot. If you happen to remove the neutrals from the neutral bar, the neutral of the hot circuit is now hot, possibly lethal, and the person doing the work is likely not aware of it. 'Voltage' is feeding from the hot breaker through any lights, appliances, etc. that are turned on and appearing at that disconnected neutral, now at a 120V potential. There is no current flowing unless something or someone touches this hot neutral and a neutral/ground. Bingo! Crispy critter. So no, it is not safe.
No, Rj is talking about a MWBC which is 2 hot legs sharing a common neutral (most commonly found as a kitchen circuit). If that 2nd neutral you disconnected and left the breaker on happens to be a MWBC, there is no normal return path for the neutral current. So power from the black hot will attempt to return through the red hot and vice versa.So, it's not that having multiple neutrals in one hole is the problem (because the electricity is all lumped together on the neutral bar), but that causing a disconnect (voltage surge?) in one of the other circuits in the same hole, especially if the juice is still on while loosening the set screw. I hope I got that right...