Hoping someone could advise me, as I have never had to deal with this type of panel before. The service coming into the house is 100amp. The panel is a split bust with 6 double pole breakers on top with 1 of them labeled main lighting which is a 60amp breaker feeding the single pole breakers/receptacles on the bottom of the panel.
Question: because the lower portion of the panel can theoretically be pulling 60 amps and the service in 100 amps service, can the upper portion of the panel, the 5 remaining double pole breaker spots, are they limited to a total of 40amps? Otherwise it would seem that you could be vulnerable to an over-current situation of pulling more than 100amps total. Is this a correct assessment? It seems 40 amps is pretty low for the double breaker positions where the range and furnace or hot water heater are attached?
Thanks for all your help
Question: because the lower portion of the panel can theoretically be pulling 60 amps and the service in 100 amps service, can the upper portion of the panel, the 5 remaining double pole breaker spots, are they limited to a total of 40amps? Otherwise it would seem that you could be vulnerable to an over-current situation of pulling more than 100amps total. Is this a correct assessment? It seems 40 amps is pretty low for the double breaker positions where the range and furnace or hot water heater are attached?