I want to add an exterior motion sensor light to an exterior motion sensor light circuit at the electrical breaker box.
My proposal is since:
1) I have material to make it to the new light from the breaker box and not further.
2) I can't double tap on the 15A GFCI circuit breaker that serves the circuit.
3) A junction box somewhere else is not really an option.
4) I am running out of breaker spaces in the breaker box.
5) I have more than enough area/volume in the breaker panel.
to run a 14-2 wire from the new light to the 15A breaker. The plan would be to splice the black wires together using an appropriate wire nut to a black pigtail and land the pigtail on the appropriate location on the GFCI. In turn, I would do the same thing with the white wires and land the white pigtail on the appropriate location on the GFCI. All derating of the NM-B cable and breaker is done. Would this meet code?
My proposal is since:
1) I have material to make it to the new light from the breaker box and not further.
2) I can't double tap on the 15A GFCI circuit breaker that serves the circuit.
3) A junction box somewhere else is not really an option.
4) I am running out of breaker spaces in the breaker box.
5) I have more than enough area/volume in the breaker panel.
to run a 14-2 wire from the new light to the 15A breaker. The plan would be to splice the black wires together using an appropriate wire nut to a black pigtail and land the pigtail on the appropriate location on the GFCI. In turn, I would do the same thing with the white wires and land the white pigtail on the appropriate location on the GFCI. All derating of the NM-B cable and breaker is done. Would this meet code?