SPace Pak Air Handler Wiring Question--208-230/60/1

7949 Views 5 Replies 4 Participants Last post by  wirenut1110
Quick question-

I currently have a 12-2 gauge wire (black, white and copper) running from the basement to the air handler up in the attic.

The Air handler calls for a 208-230/60/1 power supply.

The high voltage block on the air handler has an L1, L2, N and a grounding lug on it.

Question:
How do I connect the wire at the CB panel and the air handler?

Here is what I was thinking....

Get a 20 Amp double pole CB and connect the BLACK and WHITE lines to the CB and the copper ground to the nuetral bus bar at the CB panel. Then at the air handler, connect the black wire feed to the L1 terminal, the white wire to the L2 terminal, and the copper to grounding Lug.

Does this sound right?
1 - 2 of 6 Posts
The unit is a/c only....Im not running heat...only cooling.

Here is what the service manual says:

"Connect power supply to Terminals L1 and L2 on the high
voltage terminal block. Connect a ground wire to the
equipment ground terminal located next to the high voltage

terminal block."

It says nothing about connecting a white nuetral.

Thoughts? Im thinking I dont need 110v and the 12-2 is all that is required for the 208-230/60/1 wiring.



Here is a picture:



Attachments

See less See more