Quick question-

I currently have a 12-2 gauge wire (black, white and copper) running from the basement to the air handler up in the attic.

The Air handler calls for a 208-230/60/1 power supply.

The high voltage block on the air handler has an L1, L2, N and a grounding lug on it.

Question:
How do I connect the wire at the CB panel and the air handler?

Here is what I was thinking....

Get a 20 Amp double pole CB and connect the BLACK and WHITE lines to the CB and the copper ground to the nuetral bus bar at the CB panel. Then at the air handler, connect the black wire feed to the L1 terminal, the white wire to the L2 terminal, and the copper to grounding Lug.

Does this sound right?
 

· Electrical Contractor
Joined
·
1,054 Posts
By what you say, you're going to need a 12/3. Black to L1, Red To L2, white to N, and ground to ground.

Sounds like this unit has 240 volt loads as well as 120 volt loads. To the breaker, Black/red to breaker, white and ground to their respective bars.

The way you have it, 120 volt loads won't run.
 

· Registered
Joined
·
5 Posts
Discussion Starter · #4 · (Edited)
The unit is a/c only....Im not running heat...only cooling.

Here is what the service manual says:

"Connect power supply to Terminals L1 and L2 on the high
voltage terminal block. Connect a ground wire to the
equipment ground terminal located next to the high voltage

terminal block."

It says nothing about connecting a white nuetral.

Thoughts? Im thinking I dont need 110v and the 12-2 is all that is required for the 208-230/60/1 wiring.



Here is a picture:



 

Attachments

1 - 6 of 6 Posts