The Glycol picture is me filling the system with glycol. My system took 11 gallons, I had buckets filled with a 60/40 mix of glycol & water and buckets for when I was flushing the system with straight water before filling it with the mix. You can see my solar loop exchanger goes into the middle of the tank and comes out the bottom, heating the bottom of my tank (better for FP's). For tips on filling
- Trick the solar loop pump to kick on while also adding that inline pump to build enough head to fill the system.
- To help build up pressure, close the fill valve slowly when you want to disconnect the fill pump.
- Put a mix of 60%+ glycol/40% water. You'll have a hard time trying to get decent pressure in the loop unless you have access to a high head pump. My 2 pumps in series couldn't do it they couldn't get more than 16psi. I had to attach a garden hose from my city water & pressure (65 psi I think) to the loop and add it directly to get it up to the 25 psi I needed. However, that added straight water... but if you start with a 60% glycol/40% water you're fine diluting it a little as long as it doesn't dilute below 50/50.
- Even after running both motors purging air for 2 hours, still the automatic air valve burped air out for weeks to follow. I had to repeat attaching the garden hose to city water to get pressure back in the loop until all the air was gone. My system pressure needed to be 25psi (cold), in the beginning a good day of solar and it'd burp enough air to drop the system to 5psi when it cooled, and what I found out was my pump couldn't pump unless the system was at least 12psi else it would just spin.
One is my wife hugging the panels on my roof. I installed them flat and low so they wouldn't be seen from the front of my house. That was a mistake cause outside high temp solar insulation is $6/foot. Could I do it again, I'd have them upright and all 3 in the same row/series instead of 2 in the back and 1 in front. You have to cover them until the piping is done, they get real hot real fast in sun.
One is my controller, I think the solar loop is 153.3F and the water in my tank (the bottom that is) is 141F. That was in mid February after a couple sunny days and we didn't use much hot water. Oh, my system uses a 3 speed pump which works better with FP systems you want the heat transferred out of the loop and into the tank as fast as you can with FP's. When the temp difference is 8F it goes to low speed, at 12F or so goes to medium speed, and over 16F difference kicks into high speed. This controller also controls the solenoid valve which dumps hot water down the drain when things get too hot for the tank.
One is my PMP (or plumbing package). It has a pressure gauge, temp gauge, fill valves with a ball valve in-between, pressure/temp blow valve (you can't see), the expansion tank is screwed into the automatic air bleeder (the automatic air bleeder is a must), and a check valve.
-