i have a empty 3/4 inch blue smurf tube that i want to use to go to a J box and supply a instant hot water heater which requires 8ga and a AC unit that requires 10ga both 230volt, will all the wires fit in the 3/4 inch tube ?? and is it ok to run the 3/4 tube to a junction box and then go to the 2 different units ?
 

·
flipping slumlord
Joined
·
5,116 Posts
i have a empty 1 inch blue smurf tube that i want to use to go to a J box and supply a instant hot water heater which requires 8ga and a AC unit that requires 10ga both 230volt, will all the wires fit in the 1 inch tube ??
2 #8's and 2#10's (+ ground) will fit in 1" ENT with room to spare.
 