HI,
I recently purchased a new place. For 1 year no problem. Just this weekend though, 2 people have gotten shocked in the shower when touching either the shower head or on/off handles. I've done a lot of checking and here is what I know:
I have continuity between the plumbing (shower head, valve) and the neutral bar in my electrical panel - where all white wires are attached. (10 feet away)
I put a volt meter between the shower head or valving and the floor drain in the shower stall floor. The piping is plastic but full of water. I get 22 to 50 volts AC.
The electrical panel is 10 feet from the shower. The unit is new 200 amp service and has a heavy copper line going from the panel to a grounding rod driven in the ground about 10 feet away.
I exhaustively went through my panel, disconnecting one circuit at a time. I found that when I remove the electric water heater breaker and grounding wire from the heater to the panel, the voltage drops to 4 or 5 volts between shower plumbing and floor drain. This is with every possible electrical device running. If I shut off big items like oven, and electric base board heaters, it still stays around 4 to 5 volts AC. I get the same voltage readings stated above between shower floor drain and the common bar in the electrical box. I guess this makes sense since I have continuity between shower faucet and electrical box common bar.
If I shut the main breaker, with water heater disconnected from the elextric box, I get 0 volts for all readings when the water heater is disconnected.
I have a well. The pipe from the well to the inside of the house is plastic.
I believe I have a water heater problem with the 22 t0 50 volts showing up and was going to call the manufacturer today.
Here are my questions:
1. Should I also be concerned about the 4 to 5 volts that is always present with the electric water heater disconnected?
2. There seems to be a major problem with the water heater. What can cause the 22-50 volts to be present? If this is a failed element, can i put some safety device in place to prevent this voltage from getting to the shower?
All of these devices are withing 20 feet of each other.
Any advice on grounding, etc.. to fix this problem is appreciated. What is bonding? Should I provide further ground my plumbing?
Thanks
tbwoods
I recently purchased a new place. For 1 year no problem. Just this weekend though, 2 people have gotten shocked in the shower when touching either the shower head or on/off handles. I've done a lot of checking and here is what I know:
I have continuity between the plumbing (shower head, valve) and the neutral bar in my electrical panel - where all white wires are attached. (10 feet away)
I put a volt meter between the shower head or valving and the floor drain in the shower stall floor. The piping is plastic but full of water. I get 22 to 50 volts AC.
The electrical panel is 10 feet from the shower. The unit is new 200 amp service and has a heavy copper line going from the panel to a grounding rod driven in the ground about 10 feet away.
I exhaustively went through my panel, disconnecting one circuit at a time. I found that when I remove the electric water heater breaker and grounding wire from the heater to the panel, the voltage drops to 4 or 5 volts between shower plumbing and floor drain. This is with every possible electrical device running. If I shut off big items like oven, and electric base board heaters, it still stays around 4 to 5 volts AC. I get the same voltage readings stated above between shower floor drain and the common bar in the electrical box. I guess this makes sense since I have continuity between shower faucet and electrical box common bar.
If I shut the main breaker, with water heater disconnected from the elextric box, I get 0 volts for all readings when the water heater is disconnected.
I have a well. The pipe from the well to the inside of the house is plastic.
I believe I have a water heater problem with the 22 t0 50 volts showing up and was going to call the manufacturer today.
Here are my questions:
1. Should I also be concerned about the 4 to 5 volts that is always present with the electric water heater disconnected?
2. There seems to be a major problem with the water heater. What can cause the 22-50 volts to be present? If this is a failed element, can i put some safety device in place to prevent this voltage from getting to the shower?
All of these devices are withing 20 feet of each other.
Any advice on grounding, etc.. to fix this problem is appreciated. What is bonding? Should I provide further ground my plumbing?
Thanks