Per the drawing attached should the neut./ ground be bonded in the circuit breaker box or just the disconnect?
 

Attachments

·
Registered
Joined
·
16 Posts
Thought I agreed, but now I'm not sure... If your disconnect is unbonded, you may be ok being bonded in the panel. The key is to be bonded in one location only.
 

·
Registered
Joined
·
336 Posts
Pardon my ignorance, I'm assuming bonding means tying the neutral and ground together? Also, in the drawing it appears that in the breaker box the neutral (light wire?) is bonded to the ground wire and one of the HOT wires???? Maybe, just the way it's drawn???
 