Hi everyone,

My ex landlady called me today as she was having electrical issues and asked me to come by and see what I could find. She had low dimming lights, burning light bulbs and other issues. She is 88 years old.

Anyway I looked at what she had and here is what I discovered. This house was built in 1962. There is a breaker panel outside next to the meter base that had 2/0 or 1/0 aluminum wire to the lugs. From there someone put a #6 wire under a 70 amp circuit breaker to the inside house into her closet for all power to this house. This is a 2000 sq/ft house with all the modern conveniences we all enjoy. So this house has been operating on a 70 amp feed for a long time. How I don't know. Should be at least a 200 service. There is a bad connection between the ground on the pipe connecting the panel to the meter base. No other ground attached. There are no grounds between this panel and the house panel.

On the inside what a mess. There are only a couple of grounds but no ground that goes anywhere. There are a few Tandem breakers with what I assume are shared neutrals with 20 amp breakers but 14 ga wire. Neither box appears to be grounded or bonded correctly. This whole house has way too many receptacles and lights for this service. None of the breakers will trip or any of the GFCI outlets will trip. Most of the receptacles show reversed hot and neutrals or open ground. This is throughout most of the house.

Anyway I wanted to get some opinions on how I can help her as she is pretty old and does not have much money and I would hate to see something bad happen to her. If you guys can offer me your opinion I would appreciate it. I know the obvious answer is to call her an electrician bit the prices she was quote for the work is money she does not have. I have attached the pictures here for your review. Any help is appreciated.
 

Attachments

· Civil Engineer
Joined
·
5,832 Posts
You don't say where you are located. I don't think there is a state in the U.S. where you are legally allowed to do electrical work for someone else without an electrician's license. So unless you are willing to accept all of the potential legal consequences associated with performing work you are likely not authorized to do, I think your assistance must be limited to assisting her in finding an electrician who is willing to perform the necessary work at a fair price.
 

· Registered
Joined
·
729 Posts
Low dimming lights and burning bulbs makes me think loose connection and/or open neutral. The initial priority I would see would be measuring voltages and making sure that the service is good and that the branch with those problems is good. Then checking for MWBCs on the same leg, since someone expressed concern with that possibility. Then hunting down and fixing various problems. I would probably swap out those 20s for 15s, given the wire size.

But this should ideally and legally really be done by a professional and I am concerned that even putting the legal issues aside (you don't want to be responsible for burning down her house), you might well not have the skill set to do it yourself. What's more, is the house only her house or are there also tenants? If she is renting, she should really be fixing the electrical problems or else it is unfair to the tenant. If she is not renting, it's a 2,000 square foot house and maybe she needs to be renting a room or taking out a home equity line of credit to help cover the cost of work like this.
 

· Registered
Joined
·
775 Posts
Nothing is jumping out at me as being that terrible. Get another quote. Tell the contractor what the budget is and see how far he can go with it. Looks like it's time for a new sub panel, fix the grounding and to fix some receptacles in the house. I'd start with changing the sub based on the pictures. The service neutral is probably loose somewhere which is usually an easy fix.
As far as number 6 copper feeding the sub goes, I don't see it as an issue from the pictures.
 

· Registered
Joined
·
17 Posts
Discussion Starter · #7 ·
Thanks guys for the answers. What I probably did not make clear was the newer panel in the pictures is the main panel feeding the house. The number 6 wire you see is feeding a panel in the closet which feeds all the circuits in this house. Other words this house is being run on a number 6 wire under a 70 amp breaker.

This is a fairly nice house in a good neighborhood but boy does it have the devices inside. I honestly don't see how this house runs on a number 6 wire. For what ever reason I am unable to get any breakers to trip. All the GFCI receptacles will not failover. There are a few neutrals that are burned in the panel where they are connected to the neutral bar.

I am trying to find all that I can wrong so I can pass this along to an electrician. If it was ham and egg fix I would do it myself but given what I see I think it would be best for someone licensed. Even if I have to pay for it myself. Anyways thanks guys for those helping identify the issues you see that need fixing.
 

· Registered
Joined
·
2,513 Posts
Thanks guys for the answers. What I probably did not make clear was the newer panel in the pictures is the main panel feeding the house. The number 6 wire you see is feeding a panel in the closet which feeds all the circuits in this house. Other words this house is being run on a number 6 wire under a 70 amp breaker.

This is a fairly nice house in a good neighborhood but boy does it have the devices inside. I honestly don't see how this house runs on a number 6 wire. For what ever reason I am unable to get any breakers to trip. All the GFCI receptacles will not failover. There are a few neutrals that are burned in the panel where they are connected to the neutral bar.

I am trying to find all that I can wrong so I can pass this along to an electrician. If it was ham and egg fix I would do it myself but given what I see I think it would be best for someone licensed. Even if I have to pay for it myself. Anyways thanks guys for those helping identify the issues you see that need fixing.


Thats because every single shared neutral circuit in your home is on the same phase. I am not kidding when I say your home is close to burning down. This problem needs to be corrected ASAP, and the wire needs to be megged if not ripped out and replaced because the insulation could be damaged from over heating. This could be a several thousand dollar job.


As for the #6 wire, thats not a problem. Diversity keeps the load to 60amps and under which the wire is rated for that. On the other hand #14 carrying 30amps on the other hand is not only a code violation but a fire waiting to happen.
 

· Registered
Joined
·
17 Posts
Discussion Starter · #9 ·
Thank you Jumpstart. I kind of figured this is a very real possibility or reality. I am just afraid it will happen and she will be caught in her bedroom unable to get out.

As an example I took my wire tracer and on just one circuit is two double door refrigerators, rice cooker, coffee pot, dishwasher, a light fixture with 5 100 watt lights and one with two 100 watt lights, a range cover with fan and light plus a host of 12 duplex receptacles. Plus her puzzle light.

There are still a bunch of two prong receptacles in the house. She thought that may be a problem. The receptacles that I have examined so far that show reversed hot/neutral were in fact reversed. Easy fix. And there are the ones that show an open ground and I have not found where they are broken yet. Some have no ground at all attached. But at least I can pass this information along and it will not cost as much.

I am just curious if what she has can be made to work with proper wiring given her age as she has outlived everyone and is an only child. Again I appreciate the help and I know she does.
 

· Registered
Joined
·
2,513 Posts
Thank you Jumpstart. I kind of figured this is a very real possibility or reality. I am just afraid it will happen and she will be caught in her bedroom unable to get out.

As an example I took my wire tracer and on just one circuit is two double door refrigerators, rice cooker, coffee pot, dishwasher, a light fixture with 5 100 watt lights and one with two 100 watt lights, a range cover with fan and light plus a host of 12 duplex receptacles. Plus her puzzle light.

There are still a bunch of two prong receptacles in the house. She thought that may be a problem. The receptacles that I have examined so far that show reversed hot/neutral were in fact reversed. Easy fix. And there are the ones that show an open ground and I have not found where they are broken yet. Some have no ground at all attached. But at least I can pass this information along and it will not cost as much.

I am just curious if what she has can be made to work with proper wiring given her age as she has outlived everyone and is an only child. Again I appreciate the help and I know she does.

Per code kitchen counter top receptacles can not share a circuit with the lights and dishwasher.

With some work it can be made to work. Depending on how many circuit have been toasted and how things are wired it will vary but first the issue with the MWBC is a must above all else. They rest can technically stay since pulling to much current will just trip a breaker.
 

· Registered
Joined
·
17 Posts
Discussion Starter · #11 ·
UPDATE: okay I was able to get a good firm to come this afternoon and help straighten some of this out. They did pull new #4 wire into the first panel and ground everything proper. They also put in a new 100 amp breaker. Also all the wire issues were corrected in the second panel. Seems 4 of the existing neutrals were burnt at the connection to the neutral bar. You could just pull them away with your finger. Many wires both hot and neutral were very loose or just sticking in the attached holes.

They were able to leave the existing box as according to them breaker panels are no longer acceptable in the closet anymore. They did a nice clean job though. I will change out the receptacles and reverse the remaining receptacles reporting such a condition. The contractor would have to put a new receptacle if they opened it and had to do wire work. They said that is their company policy and was an expense she did not need.

Also there were a few lights discovered as the picture attached. Seems her house could have burned down at any time. Also in the receptacles I opened many were wired in a series connection with no grounds. There were no pigtail connections at all. Anyway I thought I would update anyone interested.
 

Attachments

· Registered
Joined
·
17 Posts
Discussion Starter · #14 ·
Hi Arrow,

It was a little scarey for a while. I too am glad this worked out for her. I would have felt bad had something happened to her. It just amazes me how this went on for so long and nothing happened. Lights are bright again and everything looks cleaned up as it should. I certainly appreciate the input from everyone and the suggestions for a solution.
 