Background: Location south central Texas
Equipment: Rudd Achiever, 12 seer, 4 ton (actual 46.5 btu) age 14 years
air handler located in attic.
Home: aprox. 2350 sq ft. (I have 2 bdrms. closed off, aprox 300 sq ft.) total 2650
Supply: (2) [email protected] [email protected] 12x12 (total of 684 sq in)
Blower: 3/4hp, 2060 [email protected] .5 static (guessing on static)
Outside temp 90F
Subcool 9 to 10 degs.
Condenser delta 20 to 22 deg
I took some temp measurements and ran thru a calculator I found on the web. (http://efficientcomfort.net/jsp/PsychroCoilCalc_Web.jsp)
CFM leaving 2060 (est)
Entering: DB 78, WB 63.5 45%rh
Leaving: DB 61.9, WB 48, 33.6rh
The calculator came up with answer:
Sensible cooling btuhr 36,237
Dehumidifying btuhr 52,167
cfm per ton 682.2
Sensible heat ratio .41
Is this what I can expect. Or is my AC not putting out like it should?
Thanks
Gary
Gruene, Tx.
Equipment: Rudd Achiever, 12 seer, 4 ton (actual 46.5 btu) age 14 years
air handler located in attic.
Home: aprox. 2350 sq ft. (I have 2 bdrms. closed off, aprox 300 sq ft.) total 2650
Supply: (2) [email protected] [email protected] 12x12 (total of 684 sq in)
Blower: 3/4hp, 2060 [email protected] .5 static (guessing on static)
Outside temp 90F
Subcool 9 to 10 degs.
Condenser delta 20 to 22 deg
I took some temp measurements and ran thru a calculator I found on the web. (http://efficientcomfort.net/jsp/PsychroCoilCalc_Web.jsp)
CFM leaving 2060 (est)
Entering: DB 78, WB 63.5 45%rh
Leaving: DB 61.9, WB 48, 33.6rh
The calculator came up with answer:
Sensible cooling btuhr 36,237
Dehumidifying btuhr 52,167
cfm per ton 682.2
Sensible heat ratio .41
Is this what I can expect. Or is my AC not putting out like it should?
Thanks
Gary
Gruene, Tx.