· Wanna Be
Joined
·
676 Posts
Discussion Starter · #1 ·
I'm no expert but I'm handy enough to try to fix this myself or learn more about what the HVAC repair person will need to fix. I recently moved into an apartment in a house so I don't know the whole history but ...

I know that as of 2 weeks ago the unit was working for both AC and heating.

it's got ceiling vents in a single story house from the 40s in Texas west of San Antonio in Uvalde. The 82 y/o owner lives alone and has done nothing but ignore it for at least a decade. Recently we had 25 degree temps and no heat so I have decided to either fix it myself or pay someone to fix it since my apartment shares the heating system with the rest of the freezing house.

This is an ancient Sears heater/ac system that is a 240 V with what looks like 4 heating elements inside a water boiler system on the first floor with an access door and an access panel. (my internet connection is too slow for pictures.)
There are two black relays with ground wires branching off to the heating elements and also 2 wires from the thermostat. I didn't touch any wiring so it's all where it should be but that doesn't mean the relays are working or that the wiring is reliable since I could immediately see two crimps that were loose. At the point I investigated I couldn't get the fan to start no matter what I did. All the breakers were on and the boiler was radiating warmth but the fan blower would not run and the motor did not sound like it was humming.

the thermostat was labeled "1997" so I changed that out after turning off the breaker at the breaker box and the breaker for the motor.

The new thermostat is a White Rogers Heater/AC dual unit that had only one difference being the R wire was terminated on the RH screw. the yellow and white and green all went to their respective screw termination. I set the anticipator dial to the same setting. I believe this is a 4 wire, type 5 thermostat.

I turned the breakers back on and the elements began to hum as they heat the water and the motor pulley turned the belt and engaged the blower fan pulley (although the bearing is shot so the internal cooling fins on the drive shaft of the motor ping loudly against the housing when it slows down. this is a separate issue of finding a 1/2 hp 240v motor to replace this ancient Franklin Electric motor) Warm air and dust is blown through the vents but nothing I do to the thermostat will turn the motor off. I lower the temperature, I turn it to cool, I turn it off, and the motor continues to blow hot air through the vents.
The only thing I noticed is that I was using a lamp as light and when I turned the temperature up or down around the 75 degree mark, which was room temperature at the time, I could hear a click in the heater compartment around the relays and the lamp would flicker slightly like a drain was taking place and then brighten back to normal. It's the same as when you have a working thermostat and you lower the temperature and it clicks and the heater shuts down. I hear the click but the motor doesn't stop.
The only way to turn the blower fan motor off is to flip the breaker switch on the heater panel that is labeled "For motor protection only"
This may have been how the owner has been turning the heater on all this time.

My tools are limited and even if I recrimped all the female blade terminals at the end of the ground wires I would still need guidance to test the relays. Should I just test for continuity? I could see some corrosion on the crimps so it could easily be a faulty wiring connection that has cut the thermostat out of the loop and shorted the system.

I will replace the motor but that's not going to solve the thermostat issue.

When I placed the compartment panel back over the assembly and flipped the motor breaker back on nothing happened so right now I'm back to square one. I didn't pinch any wires but maybe the panel is moving the wires so they are disconnecting.

any advice?
 

· In Loving Memory
Joined
·
42,671 Posts
Sounds more like you have an air handler and not a boiler.

It probably wasn't the thermostat. Relays/sequencers are probably sticking, or you didn't give then enough time to open.

Need a multimeter to test what is not working like it should.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #5 ·
You're right, it is an air handler. I call it a boiler because of the water or steam pipes I see running next to the unit but that's the boiler part of the indirect coil air handler. it has the Squirrel cage centrifugal blower fan. Amazingly it still produces heat and air conditioning so my immediate goal is to get the thermostat back in the loop. I just remembered that a few days before the blower started working non stop the cycles got very short. It would cycle on for a minute and then off. on and off and on and off. then it quit cycling and just stayed on until we turned off the breaker.

I think when I turn the thermostat off and the motor is still running after ten minutes then it's safe to say the thermostat isn't working.

It sounds like the most I can do is test the relays for a short circuit and then tighten/clean the crimps on the wires leading from the thermostat to the transformer and the relays. And if I can find the filter I'm sure that is due for a change.
 

· In Loving Memory
Joined
·
42,671 Posts
Probably a fan relay or sequencer stuck.

If your have a hydro coil in the air handler. that probably provides heat for less money then the expensive electric strip heaters do.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #7 ·
no 24v power

it's been a mystery trying to figure this out but all the repair shops are booked until after Christmas so it didn't hurt to experiment with solutions. trouble is that closest parts dealer is 140 mile round trip. So, replacing the sequencer and the heat limiter isn't possible until they open next week.
At one point the air conditioner came of full blast and I have no explanation for that since the thermostat isn't controlling anything. the A/C control wire to the house is falling apart.

I find no 24v coming from the transformer so the thermostat isn't even getting power right now. Basically the right side heating elements aren't engaging on demand. And as soon as I turn the motor breaker on all the timing elements shut off and I get cold air. if I turn it back off the elements begin to warm up. If I leave the air conditioner breaker on then it eventually kicks in. It's already 50 degrees in the house but for some reason the A/C tries to make it colder and the thermostat only goes down to 60.

I'll be replacing the sequencer and the single throw limiters and the transformer if I can find them at Graingers in San Antonio. At least the parts will be new if a service tech ever arrives to troubleshoot the problem. I suspect he'll say the unit is unserviceable.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #8 ·
Since no repairman can help me for another week I'm still trying to solve this air handler. I replaced the transformer and got the sequencer to work again but the puzzle is that the blower motor will not turn off once the sequencer is opened (shuts off). The thermostat is getting 24v but it can't turn the fan off. So, the fan relay is probably stuck closed but I'm not sure what the replacement part will be.

But the real problem is that even with 24v going through the thermostat, the fan blowing AND 120 v going to each timing coil and heating element terminal and the sequencer's 4 terminals closed, NO HOT AIR IS BEING PRODUCED. I could live with manually shutting the blower off but there is no heat. As soon as the blower comes on all the heat disappears. The A/C isn't coming on but neither is the heat. Only when I shut down the blower motor does something warm up inside the sheet metal compartment. It never gets hot but at least the metal warms up. 110v goes directly to the left side terminals that a schematic tells me is the timing coils. Are they the same thing as the heating terminals? THe left side terminals come directly from the main power jumper terminals. The right side terminals are jumped through the sequencer and only direct 110v to those right side terminals when 24 v is channeled through the bottom terminals. But that only happens when I turn the thermostat on AND manually flip the breaker to the motor. But as I said, when I do that the power goes to the terminals but there's no heat. It's like I'm visually seeing things work but the end result is 50 degree wind chill through the vents.

SO, let's figure I'll fix or replace the fan relay if I can find a replacement (it's that black box next to the transformer in the picture). Are the heating elements themselves burned out? There are 5 heating elements total but the top ones are not connected since the sequencer only has 4 terminals. Could all 4 be burned out? The transformer, fan relay, limiter switch, thermostat, sequencer and every heating element all failed in the same week? Sears service dept gave me an appointment for one week from now with 30 degree nights predicted so I'm prepared to drive to the big city to buy a fan relay and heating elements and motor...but if anyone has any suggestions or even a diagram of what I'm looking at then I would be grateful. For instance, is the heating element warming up a container of water? OR does air blow over the elements and that's all it does. What else needs to be serviced in the heating part of this air handler?
 

· In Loving Memory
Joined
·
42,671 Posts
Check for 240 volts across the sequencer when the stat is calling for heat. And when you have the fan turned off.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #10 · (Edited)
I was getting 118v across the sequencer and was puzzled until I took the heating elements out and they were all burnt out except for the bottom one, which has a big kink in it, and the top one which was a spare. So, the coil itself was broken on three of them. The warmth I felt was the one working element turning on. I'm not sure why it was warming up with the stat turned off but that's another problem. the hunt begins for replacement elements.
I tried to shortcut the coil from one terminal to another and it worked for a few minutes until it burned out also. For that minute I did get 240 across the sequencer...so at least that works.

The fan relay still doesn't stop the fan even though I took that apart and filed/polished the contacts. The relay clicks when I turn the stat fan switch on and off but the fan never stops. The relay has one wire joined with the green wire from the stat and another wire joined with the A/C control wire. Even when I turn the A/C breaker off the fan keeps going. and I bang on the relay with a mallet and it won't shut off.

My advice is when you live this far from a parts supplier then build a fireplace.

Update: No one in my part of Texas has this part so if anyone has a parts supplier who deals with antique Sears Heating systems then let me know. I need three of them. The unit model # is 493.58703 but I don't have a part number for the heating element. It's 5000w 240V. It was a central air conditioning unit but that's been replaced by one that sits outside. The heating parts are original. This might be the end of the line. I already tried to stretch the coil and it just breaks and crumbles from age. Solder will melt again when it gets hot. Any other ideas to bridge the break in the slinky element?
another model number is: heating furnace 126646.

This evening I replaced the sequencer and a limiter sensor and then stretched the heating element to reach the terminals but it won't last because the coil is aged and brittle and it decreases the actual surface area of the coil itself. But it works and there is emergency central heating now. SO the only puzzle I can't solve is why the fan won't stop. The routing is a 120v goes into the motor breaker switch and exits into the + red wire of the motor. The - black motor lead branches off with one branch going to an upper limit sensor and the other branch going to the fan relay. Both of these branches have 120v present when the breaker to the whole system is on. So obviously the moment I switch the breaker of the motor back on then it power on and turns no matter if the stat is switched off or the fan is switched to auto. The other top lead to the relay is a 120v from the main terminal screw cluster. One bottom lead from the relay joins with the green wire from the thermostat that's in the G terminal. Switching the fan switch on the stat makes a clicking in the relay but nothing happens to the fan. And the other lead joins with the A/C control wires.

I suspect someone hardwired the motor to stay on because a sensor or relay broke but why would they hard wire it through a limiter sensor? A new fan relay would help but I'm hunting for that now.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #14 · (Edited)
Yes, that restring kit looks like what I need. I asked at Ace hardware, Graingers and another electric supply store and none suggested that item but I suspected it existed. Only I didn't know what it would be called.
My budget on this project was around $200.
$34 new thermostat
$40 new transformer
$40 sequencer and limit sensor
$8 x 4 restring kits = $40*

IF I can find the fan relay then the only thing left is an HVAC class to teach me how to wire it all together.

Oh, I forgot the $150 to replace the motor. Shoot. I'm going to be over budget. It's a $300 job in parts alone. Labor doesn't count since I am learning everything from you all.

* probably $20 each so $80 total.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #16 ·
the only thing I have to help me wire it is a worn schematic on the back of an access panel. I'm going to take a picture of it and post it here because it's like an archaeological hieroglyph that will be understood only by people who voted for or against Eisenhower. The owner's manual looks like it was made by the same publishers of the "What you need to know about the Atom Bomb." pamphlet. unfortunately the manual is for the long replaced A/C unit.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #17 · (Edited)
For the first time the fan switch on the thermostat worked in the sense that when I turned the switch to on, the fan came on. but when I turned it to auto and turned the heat on the fan never came on. I can manually turn the fan on with the stat switch but it's still giving me a headache. I really suspect it's either scrap the whole unit and start baking brownies to fund raise or personally rig the whole thing to work because no licensed repairman would work on it. I saw sparks from the insulated mount of the squirrel cage which leads me to think the whole frame is shorting to 120v.
the sequencer is represented in this picture as clutch coil "timer". or maybe the sequencer was a later upgrade in 1980. one thing that bothers me is the transformer that I Replaced had 40va printed on it. so it wasn't original but that's the specs of the new one. does it matter? ANother problem with this schematic is the stat is not accurate. I guess in 1958 the fan control was part of the unit and not on the stat. Now there is a yellow A/C control wire and a Green fan relay.


here's a picture of the fan relay. it's the only thing I haven't replaced because I can't find a match.
 

· Wanna Be
Joined
·
676 Posts
Discussion Starter · #19 · (Edited)
I investigated and found that two of the elements that I had stretched and reattached had both burned out again and then the dangling part drooped down so it touched the metal cage that holds the ceramic posts. so the element was still working because it was shorting directly to the frame of the heater. Another reason why there is no fixing a broken heater element. So I took those two elements out and am left with two of four that never broke to begin with.

but I don't know enough about these limiters and relays and the schematic is only partly up to date. all the info has been baked off one of the sensors so I don't even know if I replaced it with the right part. The heat comes on but the fan won't turn on automatically. I took apart a limit switch that says "off at 200 degrees" and it's ancient also with this lever system that pushes a small pin into the switch. The pin is stuck depressed but that means it's stuck in the closed position since I don't think the unit ever got over 200 degrees.

I think when I turn the fan switch at the stat to ON that overrides the heat setting so it immediately turns the heat off.* reading the stat manual tells me that actually when the fan is switched on and the heat is selected the "heating system cycles from thermostat; fan runs continuously." So, it's a puzzle why the heating elements shut down when I turn the fan to on. I suspect a miswiring.

according to the motor label and the schematic it's a 240v motor. So I'm thinking of wiring the black motor wire to the load side of the sequencer so when the heat is on, the fan is on. no limiter sensors, but I don't know how to complete the circuit once I remove that part. The black motor line branches off all over the place, to one sensor then to the limit switch that's stuck closed, then to the transformer. And the same branch goes directly to the fan relay but the color codes are a mess as someone used a chunk of the brown relay wire to bridge the distance between the black motor wire and the red relay wire.

It's possible the relay and the limiter switches have failed in a way that prevents the motor from turning on when the heat comes on but the way it acts makes me think something is wired backward. Also, it's obvious only amateurs like me have worked on this unit in the past 40 years. The killer is that it's merely a glorified space heater and it really is a boat anchor but the realities of a fixed income of the owner and general poverty of everyone involved makes me not want to give up yet.

I'll restring the elements, replace the relay and the limiter switches but I still need help wiring it.

I can post a picture of a labeled and numbered schematic of what actually exists in the unit. If anyone is up to the challenge then maybe we can team up and wire it by the book.

Today I moved the thermostat and re-stripped all the wires. I have crimping tools and blade terminations and new 10ga wire at the hardware store. I've tested for continuity at the terminals but I can't vouch for the resistance.

The only reason I've gone this far is because Jan 7th is the earliest a serviceman can see it. And I know he's going to charge $100 to tell me it can't be fixed so I'm trying to fix it myself and cancel the appointment. And even if it can be fixed he'll be at least a week ordering the parts. I really feel I can learn basic HVAC wiring in 2 weeks with a little tutoring so it makes no sense to wait. At least we found a few space heaters for the cold nights.

In case anyone is wondering I replaced the thermostat with a white rodgers 350 that replaces everything but a hydronic zone heat stat. I don't think the old one was broken but now I'm not sure either thermostat is right for this unit because of its age. The same problem happens with both thermostats. When switched to Heat/Auto the heat comes on but the fan is off. I've got the heat anticipator set to .4 amps because that's what the old stat was set for but I can't find any stamp for the actual rating.
 

· In Loving Memory
Joined
·
42,671 Posts
Problem was probably the fan relay or a sequencer, not the stat.

Won't learn HVAC wiring 101 in 2 weeks. but might be able to rewire your unit up to work with the new parts.

I'd probably just wire the blower up to run 24/7, and let the stat control the 2 remaining strips, until I had the parts and restring kits.
 