Don't take my word for it and hopefully the more seasoned pro's will chime in, but I believe 4 #2's w/ 40% fill would be allowable in an 1 1/4" pipe. I just ran 2-2-2-4 in 1 1/2" over 250 feet and it was an easy pull.
Yep. Like robertmee pointed out, it might be overkill, but not a bad thing.Am I correct in that I can use 2" SCH 40 PVC for this project?
Yep.Do I really need grounding rods for this install?
OK as they're larger than #6. AFAIK the EGC has to be marked anywhere it's accessible, even if not the cable termination. Probably not an issue for your run.Second question, all four wires will be black, is it ok for me to utilize colored electrical tape to mark each one (red, white, green, black)?
Actually I thought the code said something like the wire to the ground rods is not required to be any larger than #6. Water pipe bond is sized to the service and may be bigger than #6.#6 is the code minimum for the ground rod wire.
Rob
For 100 amp, a #8 is code minimum for the ground. You can go larger, but there's no need to. The #2s are about right for the hots and neutral though. You can use colored tape on anything larger than #6, according to code. Almost all of my work is inspected, and I can't even count the number of #6s and #8s I've used colored tape on, and have never had a problem.
2" is plenty for this run. If there are only two 90s, it'll be an easy pull. If there are 4, it'll still be fairly easy.
If it were me, I'd install a 1" in the trench while it is open. Just stub it up somewhere, you might want a phone or something else out there someday.
You'll need at least one ground rod to be legal, two if your soil doesn't conduct well. There's no requirement for more than two though. Around here, one rod will give about 5-10 ohms. 25 is the code maximum. #6 is the code minimum for the ground rod wire.
Rob
#2 75C is good for 115A if you don't need to derate (I'm looking at table 310.16).I figured #2 was bigger than I needed, but since I bought a 1000' spool to run the 100 amp subpanel to the basement and the barn, I wanted to ensure I never had a voltage drop problem.
I'm looking at table 310.16, NEC 2008 -- where are you getting 100A as an allowed ampacity of #6?You can use all #6 if you have enough wire. For the ground too.
Sorry Scott and the OP. I meant for the EGC. He is using #2cu for the CCC's.I'm looking at table 310.16, NEC 2008 -- where are you getting 100A as an allowed ampacity of #6?
Actually it really is a minimum...the gec to the electrode if it is a rod must be at least 6 awg copper but can be larger if you want.....Actually I thought the code said something like the wire to the ground rods is not required to be any larger than #6. Water pipe bond is sized to the service and may be bigger than #6.
Stubbie,I'm surprised that no one brought up NEC 250.122(B)....![]()
I disagree. 1 1/2 Is already plenty overkill. Spend the money saved on a couple 1 inchesShould have stuck with 2".
Bigger is generally better.:thumbup: