Here is 430.6(A)(1) and other applicable sections based on a 1.5 HP, 230V motor;
430.6(A) 1 states;
(1) Table Values. Other than for motors built for low speeds (less than 1200 RPM) or high torques, and for multispeed motors, the values given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250 shall be used to determine the ampacity of conductors or ampere ratings of switches, branch-circuit short-circuit and ground-fault protection, instead of the actual current rating marked on the motor nameplate. Where a motor is marked in amperes, but not horsepower, the horsepower rating shall be assumed to be that corresponding to the value given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250, interpolated if necessary. Motors built for low speeds (less than 1200 RPM) or high torques may have higher full-load currents, and multispeed motors will have full-load current varying with speed, in which case the nameplate current ratings shall be used.
Table 430.248 indicates 10 amps for a 230V 1.5 HP single phase motor.
430.22(A) General states;
(A) General. Conductors that supply a single motor used in a continuous duty application shall have an ampacity of not less than 125 percent of the motor’s full-load current rating as determined by 430.6(A)(1).
10A x 125% = 12.5A
Table 310.16 indicates #14AWG is rate for 20A.
Now before you get your panties in a bunch the asterisk refers us to the bottom of Table 310.16 where it states: See 240.4(D).
240.4(D) states;
(D) Small Conductors. Unless specifically permitted in 240.4(E) or (G), the overcurrent protection shall not exceed that required by (D)(1) through (D)(7) after any correction factors for ambient temperature and number of conductors have been applied.
240.4(E) refers to tap conductors which is not applicable here. However, 240.4(G) is a table and tells us that Article 430 applies for motor branch circuit conductors. This means that #14 AWG is specifically permitted to be used for conductors supplying this motor load.
Next we look at sizing the ground fault, short circuit, overcurrent protective device.
430.52 states;
430.52 Rating or Setting for Individual Motor Circuit.
(A) General. The motor branch-circuit short-circuit and ground-fault protective device shall comply with 430.52(B) and either 430.52(C) or (D), as applicable.
(C) Rating or Setting.
(1) In Accordance with Table 430.52. A protective device that has a rating or setting not exceeding the value calculated according to the values given in Table 430.52 shall be used. (Also read the exception.)
Table 430.52 states that for an inverse time circuit breaker (ITCB) protecting a single phase motor it is to be sized at 250% of the FLA as stated in Table 430.248.
10A x 250% = 25A
Based on the above calculation a 25A ITCB is correct.
If the motor fails to start and run then 430.52(C) (1) Exception No. 2(c) can be applied which states;
(c) The rating of an inverse time circuit breaker shall be permitted to be increased but shall in no case exceed 400 percent for full-load currents of 100 amperes or less or 300 percent for full-load currents greater than 100 amperes.
10A x 400% = 40A
Since we can’t exceed 400% of the motor FLA we have a 40A ITCB on a piece of #14 AWG conductor.
The real kicker is that if this was a pool filter motor it is code compliant.