no you cant parallel breaker output as the load will not be shared equally (internal resistance of each breaker is never the same) so one breaker may have 80 amp and the other one 40.
The bend radius is limited by the gutter space, it has nothing to do with stab rating.Side note, I was reading up on other scenarios of panels only being rated for a max circuit branch of 90 or 100amps, but the reason being due to bend space of that required size conductor, not necessarily that the panel itself couldn't handle it.
( bold highlight by me)Most Square D QO or HOMELINE panels are supplied with "double row" bus
bar construction. This means that the bus bars will have branch circuit
breakers plugged onto the bus bars from the left and from the right.
The "bus stab", "bus finger" or even "connector finger" is the point on
the bus bar that the branch circuit breakers electrically connect to the
bus bar. For instance, a 40 space panel will have 20 "bus stabs". The
bus stabs accept circuit breakers from both sides, providing the
capability to plug on 40 1-pole circuit breakers.
If your panel is restricted to 125 ampere per bus stab, that means that
you cannot put two breakers onto that bus stab (one from each side)
that exceed 125 amperes between them. For instance, you could place two
60 ampere breakers (60A+60A=120A) across from one another on the same
bus stab(s), but you could not place two 70 ampere breakers
(70A+70A=140A) across from one another on the same bus stab(s).
This restriction is not applied to all QO or HOMELINE panels. The
restrictions are applied only when we must limit the total amperage on a
stab to pass applicable UL heat rise tests.
I hope that this has satisfactorily answered your questions. Please let
me know if you need anything further on this subject.
Regards,
Rick Snapp
Product Technical Support Group
Square D Company - Lexington Plant