I have a Rheem Prestige 3 ton 2 stage that was installed in May 2011. The outside unit keeps shutting off due to error code 29 (high pressure lock out) or something along those lines. When the compressor kicks on is the fan supposed to start up at the same time. I have been noticing the fan does not spin at all some times (about once a day it does not). When I notice it I will spin the blades with a stick and it will kick on and go. About once a day I get the error code 29 and have to reset PC board. I have two capacitors in the control box and dont know which one is the starting capacitor. One is sticking down through the control box. The other is a smaller one inside the box. But the 88-106MFD 330V capacitor has white stuff coming out of it. Would this more then likely be my problem? If so where would be a good place to pick one up. I would appreciate any info you may have.
 

· Registered
Joined
·
16 Posts
Discussion Starter · #4 · (Edited)

· Registered
Joined
·
16 Posts
Discussion Starter · #6 · (Edited)
Sorry for such a long delay in replay. I have now changed both capacitors, air filter and cleaned the coils. Still about once a week the outside unit trips with error code 29L (high pressure switch trip). #1 thing on the list says "condenser fan is not running". I have watched the control board and the red "call" light comes on and the compressor will kick on. But the condenser fan will not. After about 1 1/2 to 2 minutes it will kick on. Sometimes the fan will never kick on and I will have to spin the blades by hand and it will kick on and go. I'm thinking that is whats causing my high pressure. But what could be causing it? Is there supposed to be a delay between compressor and fan kicking on?

Dont know if it matters but its a 3 ton, 2 stage with heat pump.
 

· Registered
Joined
·
2,880 Posts
On the two stage there is a delay with the fan coming on. But you should never have to push the motor to start it. If you have the correct capacitor and the correct wiring it could be the fan motor. I have also seen some scroll compressors start and trip the high pressure switch on start up a few times, not many. You may need to have a good service tech check it out to determine what's wrong so you don't have to throw any more parts at it. Should be a ten year parts warranty as well
 

· Registered
Joined
·
16 Posts
Discussion Starter · #8 ·
This system is just over 5 years old. Already had to replace fan and coils in attic. The place that installled it is no longer in buisness. So i had to pay labor. I have had 2 companys come out to check it out and both said they are not familiar with this system. We live in the middle of no where and its hard to get a good tech. Any ideas how to find someone?
 

· Registered
Joined
·
2,880 Posts
I would say, start with neighbors, friends etc.. Labor would not be included but Rheem will honor the warranty with a licensed tech. It's only ten years if it was registered. Otherwise it's 5. The ones I have seen with trouble on start up were indeed 3 tons. You might want to mention for him to check that on startup. But if you are having to push motor to start I am suspecting, motor, wiring or capacitir
 

· Registered
Joined
·
16 Posts
Discussion Starter · #10 ·
Well it very well could be the delay your talking about. By the time i catch it might be when its supposed to kick on. And im really not doing anything LoL. Reading the cover says it will try 3 times then trip. Really wondering if it is the compressor. Its very loud when it kicks on. I will continue to look for a good tech.
 

· Registered
Joined
·
15,740 Posts
Maybe i missed it, but what is the model number? I'm not super familiar with their previous lineups, but somewhere in that range they started to use ecm condenser fan motors. (i didn't see a picture with the run cap installed so it's hard to guess which type it is)

ECMs are much more expensive and may have other problems so it's important for us to identify the motor type.

Cheers!
 

· Registered
Joined
·
15,740 Posts
How many terminals on that cap are used? 2 or 3. Ie. Is one terminal left empty?

I see at least once reference to an ecm on the parts list for that unit.

That cap doesn't look so new. Old picture? It also only shows 1 capacitance rating, so it's likely not a dual cap. More evidence towards an ecm.

Cheers!
 

· Registered
Joined
·
16 Posts
Discussion Starter · #15 · (Edited)
How many terminals on that cap are used? 2 or 3. Ie. Is one terminal left empty?

Only two terminals on the cap and both being used. Single 40uF

I see at least once reference to an ecm on the parts list for that unit.

That cap doesn't look so new. Old picture? It also only shows 1 capacitance rating, so it's likely not a dual cap. More evidence towards an ecm.

This was the pic of the old one. When I changed both caps I got the same brand and model number as the original one.

Cheers!
The fan motor has over 5 wires running to it if that matters. So it sounds like the fan might be the problem? Will try and get a pic of fan motor when I get home.
 

· Registered
Joined
·
15,740 Posts
So it's an ecm. There's supposed to be an led code for the ecm failure. Not sure why it's 29. I couldn't find that code in the manual. (23 for HP)

That's the bad news. Good news is that it's a 2 speed ecm. More expensive then regular motors but cheaper then the specialized ecms. It's also replaceable with a generic.

With that said, you have 3 wires from that motor don't to connector e11. Can you measure the voltage between:
1(white) and 5(black)
3(yellow) and 5
6(red) and 5.

I think your low speed may be working but not the high speed. We need to figure out if it's the board or the motor controller. (change the wrong one and your problem will still be there)

Cheers!
 

· Registered
Joined
·
16 Posts
Discussion Starter · #17 ·
I will try and get the voltage readings tonight.

This problem only happens about once a week or sometimes 2 weeks or even once a month. I know the high speed works because I can hear it kick into high all the time. East Texas has been over 100 degrees this past month. Will this unit start in high speed? The only code that I get on the LCD is 29L. Seems like the motor is not getting the signal or the fan is too weak to start up on its own at times. When I spin it by hand it will kick on and go. But I know nothing about A/C.
 