So I just replaced the inside blower motor and capacitor and I plug everything back on, turn power back on and now the outside unit will not turn on. The inside blower works now, so that's a plus.... I double checked the connections and all looks good. I even reset the outside fuse and still no luck. Any ideas? Thanks!
 

· Registered
Joined
·
17,822 Posts
Check the low voltage connections at the board. Tighten them.

One wire going to C, other to Y for the outdoor unit.

Jumper R and Y at the board and see if the condenser kicks in, door safety switch depressed.
 

· Registered
Joined
·
2 Posts
Discussion Starter · #3 ·
Thank you for the quick reply. You are a life saver! Happy (and cool) wife = happy life! Good thing I took plenty of pictures. The top connection originally had red and yellow and after another inspection the yellow wire came loose. Connected it back up and tightened the others and it came back on! Thanks again for the help!




Check the low voltage connections at the board. Tighten them.

One wire going to C, other to Y for the outdoor unit.

Jumper R and Y at the board and see if the condenser kicks in, door safety switch depressed.
 