Hi everybody, I was visiting my sister in South Carolina earlier this week and heard her Heat Pump buzzing while not in operation. The fixxer upper in me said, that doesn't seem right. A little googling and quick trial and error pointed me to the reversing valve coil. With the 220v pulled, the buzzing was still there and when switching the thermostat to off, it went away. Her unit is a 12-14 year old Nordyne FT3BC-036K and I located the model number for the reversing valve coil assembly from and online manual. I came up with PN 668770. I also read it could be the transformer and frantically searched locally for a 110v to 24v transformer and could only come up with one for a doorbell. I did actually get ready to install the new transformer but the one in the fan/heater enclosure was actually a 220 to 24v transformer fed from the board. So no ability to replace that while I was there.

I did some further googling and somehow came up with a cross reference (in an Ebay auction) of the 668770 Coil to PN669343 and was able to find that on eBay and the seller said he could hurry up and ship it out to me so I could repair it before I left her house to return to Chicago. Once it showed up, it was a good .5" -.75" longer (and actually the PN was 6693430) than the one that was on the unit (same diameter hole for the shaft though). I did some more googling to see if there would be any problem using a longer Coil on the valve and my results were inconclusive. The coil that arrived was a "Ranco L30-12 Used on V1-V12 50/60hz 6/4W N-3072 A02". The only differences I could find besides the length is that it didn't have a metal frame around it like the original. I really couldn't read anything on the old coil since all the letters were worn off and I can't even find the Nordyne 668767 anywhere on the internet to even research or buy!

I tested the new coil while energized and placed it on the stem and could hear the valve actuating. So I thought, I should be good.

Not wanting to put everything back together without fixing it, I put the new coil on, and bought a little bit longer screw and used a couple washers and a lock washer so I could make it snug without bottoming the screw out in the stem.


AC ran fine the rest of the day, the next day and a third day. On the fourth day, I got a call from my sister saying the Thermostat was blank. At first I thought it had to be a huge coincidence and told her to replace the battery. She said there wasn't a battery and she was right. It was a Robertshaw 9420 and it ran solely off the 24v transformer. She doesn't have a Multimeter to check if she is getting 24v across C and R but my guess is that she isn't and that is why the thermostat is blank.

Sorry for all the lead up, but I thought more info was better in this situation. I did wiggle some of the wires connections on the AC control board because the thing looked like it had pretty significant aging and I wanted to make sure there was good electrical connection between all the connectors just in case that was part of the reason for the buzzing. If I was there, I could troubleshoot it and get it back going I'm sure of it. But from 1000 miles away, I am trying to help my sister from paying a lot of money because I wanted to get rid of a buzzing noise!

Did the slightly larger coil burn out the transformer or did replacing the coil finally push the transformer to die? Or is this all a coincidence and the transformer just decided to die 3 days after this repair?
See less See more
1 - 11 of 11 Posts
Your sister (or you) might be paying a lot of money. A loose or poor fitting coil can overheat and have a meltdown. I've seen them damage the valve shaft to a point the valve couldn't be salvaged.
The thermostat is blank likely because the control fuse tripped and/or the transformer shorted.
Someone proficient with electricity will need to diagnose it on site, with a meter.
Don't buy HVAC parts off eBay. You should have ordered the parts from the manufacturer.
Check TR 240 vAC in 24vAC out. Check control board for 3 or 5 amp fuse. And or You may have an inline fuse?? On the control board sometimes loose, cracked solder joint = which may give low volts to RV solenoid. Check for Loose corroded T/S wires. Check voltage @ RV solenoid. Put screwdriver into old solenoid apply 24VAC - solenoid will be like a magnet .. Unit should run in heat with solenoid disconnected.
Your sister (or you) might be paying a lot of money. A loose or poor fitting coil can overheat and have a meltdown. I've seen them damage the valve shaft to a point the valve couldn't be salvaged.
The thermostat is blank likely because the control fuse tripped and/or the transformer shorted.
Someone proficient with electricity will need to diagnose it on site, with a meter.
Don't buy HVAC parts off eBay. You should have ordered the parts from the manufacturer.
I already stated that I couldn't find the part online anywhere. It wasn't loose at all, it was exactly the same diameter hole for the shaft and worked for 3 days. It didn't melt down, it still looks brand new.
Check TR 240 vAC in 24vAC out. Check control board for 3 or 5 amp fuse. And or You may have an inline fuse?? On the control board sometimes loose, cracked solder joint = which may give low volts to RV solenoid. Check for Loose corroded T/S wires. Check voltage @ RV solenoid. Put screwdriver into old solenoid apply 24VAC - solenoid will be like a magnet .. Unit should run in heat with solenoid disconnected.
I had my sister order a multimeter. I definitely can comment on the fact that the T/S wires were super cruddy and corroded at the AC unit outside. I actually tried to take off the wire but on one hoping to strip it back and reconnect but it just snapped. I ended up having to wrap them together and put electrical tape over them.

I know I could figure it out if I was there. This just sucks that I have to do this long distance.

Did the bigger coil kill the transformer (if it isn't putting out 24v) or is that just a coincidence?

I'll report back on Sunday if I can get my sister to climb up in her attic and check some of this stuff.
I already stated that I couldn't find the part online anywhere. It wasn't loose at all, it was exactly the same diameter hole for the shaft and worked for 3 days. It didn't melt down, it still looks brand new.
You can't just stick whatever coil you can find on a valve and expect it to work. Exposed coil with no load will overheat and fail.
Your sister will have to deal with live voltage to test the unit, I hope she's ok with that.
Multimeter Harbor freight Tools $6--$8.00 - Think about- Put your E-mail address in profile someone may give out phone # & help over the phone 3 way call??-- You lost your 24vac. Your sister look @ you tube furnaceman- how to test TR etc. you may need 3 - 5 amp circuit breaker (reset-able) Don't let this happen ---
--
You tube Grayfurnaceman -- rev valves - rev valve solenoid- trans former
It ended up being a fuse on the board. I talked my sister through putting the old coil back on and a service guy found the fuse.

I wonder if the larger coil blew the fuse or just my general moving stuff around made a bad connection.
It ended up being a fuse on the board. I talked my sister through putting the old coil back on and a service guy found the fuse.

I wonder if the larger coil blew the fuse or just my general moving stuff around made a bad connection.
The different coil probably caused an elevated amp draw, or overheated and shorted. The coil needs to match the valve it's attached to.