Discussion Starter · #1 ·
I am doing some remodeling and I wanted to replace a 25 year old light with a recessed light and add a second (actually wanted to do 3 lights in one string - sorry not an electrician so not sure the name for this, but it is a daisy chain of 3 lights on the existing wire/switch) recessed light. I removed the old light fixture (picture below) and added a new 6" inch led recessed light. All went well - the light turned on. I then added a second light by adding additional wire (Type NM-B 12/2), everything is on 12 guage as I have 20 amp breakers, the length of the new wire is about 8 feet. I used the quick connects that came with the new light fixtures - easy to connect; black to black, white to white, green to ground. The second light is a 4" led recessed light. I turned the light switch on to check the second connection and the breaker was tripped.

The old light has a 60 watt max lamp warning. The 2 new light fixtures, as they are LED use 14 watts (6" light) and 9 watts (4" light) I figured the combined watts, as they do not exceed 60 watts would not be a problem. Adding the 3rd 4" recessed light, an additional 9 watts, for a total of 32 watts would still not be a problem.

But I don't know why adding the second light caused the breaker to trip.

Any ideas?, Your help is greatly appreciated. Photos attached.
 

Attachments

· Registered
Joined
·
628 Posts
The breaker tripped because you have a dead short.



Make certain that you are creating a parallel circuit. A daisy chain is more of a series circuit. Use an electrical meter to measure the voltage on the line side. Draw out your parallel circuit on paper and follow that.
 

· Registered
Joined
·
4,127 Posts
Could be many things. Need to examine your connections closely.

Years ago I was replacing all the receptacles and switches at an old house and once I made all the changes and flipped the breaker on it trips.

I was surprised because I double & triple checked all my connections and I knew nothing was loose. After some trouble shooting I narrowed it down to one box being the culprit, and the breaker would trip only when the receptacle was securely mounted on the metal box. If I loosen the receptacle from the box everything works.

Turned out it was the mounting screws. I had an EMT conduit coming in from the top center hole of the box, the conduit had multiple solid #12 conductors, and the conductors are interwined at the entrance of the conduit when the longer than normal (because that box was recessed a bit more) mounting screw hit the conductors, my continuing tightening caused it to pierce the insulation and made contact with the bare copper. Once I loosened that screw, everything worked again. What's the chance of that?
 

· Registered
Joined
·
87 Posts
Discussion Starter · #5 ·
Thank to all for replying. I had a similar issue with an exhaust fan tripping the breaker - it was due to the clamp being on too tight. I am going to check the clamps on this problem to see if it is the same problem. I'll update later today. Everyone stay safe out there!
 