Picture shows what I'm doing - this will be inspected as it is part of a renovation that includes electric permit.

Goal is light shining from inside window boxes (cornices) onto ceiling, maybe dimly down curtains.

Home structure is concrete block, brick facade. Inside is 3/4" furring strips supporting 1/2" drywall
The space above the window is small vertically so I can't fit an exterior/water tight receptacle box.

The circuit will be on a gfci breaker.

Thoughts/suggestions on doing this better, maybe making the receptacle somewhat waterproof, whether this will pass inspection :) ?

Thanks
Bob
 

Attachments

· Registered
Joined
·
30 Posts
Discussion Starter · #4 ·
Yeah - thanks for catching that. This box is 13 cu in. I guess I can't even put two side by side, one for receptacle and single 14/2, one for three 14/2.
This sucks. Have to see what I can do here.
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts
WHY waterproof?
WHY a GFI breaker?

It's an almost certainty that this will require AFCI protection.
 

· Registered
Joined
·
11,194 Posts
2014 NEC calls for AFCI on most of the 120v circuits. Kitchen and bath have exceptions, but it doesn't look like you fall under those.
You are modifying a circuit, and need to bring it up to current code, assuming your area is on 2014 NEC.
 

· Licensed Electrical Cont.
Joined
·
7,829 Posts