Discussion Starter #1 (Edited)
Just pulled six 20A 12-2 home runs for the kitchen remod. Want to make sure I pulled these correctly before I consider the rough-in complete. Pulled two countertop small appliance, one dishwasher/garbage disposal, one refrigerator, one lighting.

The sixth serves a single counter-top receptacle where I plan to plug in my countertop microwave (1200W). I ran the gas stove pilot light receptacle and range hood light/fan power off this circuit. I figured this was logical since a micro/hood combo gets its own circuit.

Is this legal, or do I need to fix this before I continue? Still have plenty of wire hanging out of the boxes if I need to make changes.
 

·
"So I Re-Wired It"
Joined
·
258 Posts
Micro Hood must have dedicated circuit. Countertop one i dont think its "required"
1200 watt is a decent size, if its no trouble to give it a separate circuit, why not do it?:)
 

·
Licensed Electrician
Joined
·
4,352 Posts
I would put it on a separate 20A circuit...the range hood that is. It is probably going to be overkill right now, but its going to come in real handy when you decide to install an over the range micro.
 
  • Like
Reactions: Thadius856

·
E2 Electrician
Joined
·
5,655 Posts
The sixth serves a single counter-top receptacle where I plan to plug in my countertop microwave (1200W). I ran the gas stove pilot light receptacle and range hood light/fan power off this circuit. I figured this was logical since a micro/hood combo gets its own circuit.
You cant have the hood on this circuit, put the hood on the lighting circuit, the stove is legit. :)
 

·
"So I Re-Wired It"
Joined
·
258 Posts
re-read the post. misunderstood. thought he had a MicroHood on dedicated, and also a Counter Microwave on another countertop circuit.
 

·
Licensed Electrician
Joined
·
4,352 Posts
Why cant we just answer the code question?

No, the third small appliance circuit you pulled to the countertop cannot serve the hood unit....
Could you point to a code reference on that?
 
  • Like
Reactions: Thadius856

·
Licensed Electrician
Joined
·
4,352 Posts
Right back at you, tell me where it is allowed....


But since you asked, 210.52 (B)(2) No Other outlets. The two or MORE small-appliance branch circuits shall have no other outlets...
One word missed in a different code messed my logic up. I agree with your assessment.
 

·
Registered
Joined
·
924 Posts
Discussion Starter #12
Read all this twice and not sure I understand fully. I think the concensus is:

Move gas range to one of the small appliance circuits.
Move range hood to lighting circuit.

Now have 3 small appliance circuits, the 3rd one to the single countertop receptacle for the plug in countertop microwave.

If I ever decide to change to micro hood some day down the road, pull 3rd small appliance back up the wall cavity, remove hood from lighting circuit, and drop the spare circuit back down to dedicate to microhood.

Is this correct?
 

·
"So I Re-Wired It"
Joined
·
258 Posts
Minimum 2 small appliance outlets in kitchen. These outlets shall not have any other outlets. (Dedicated)
Just run a dedicated circuit for the countertop microwave.
Personally i would run another dedicated outlet for the range hood. I dont believe it is considered a small appliance.
Although it may not be required, to do it now would save time and money later.

The gas range is not considered a small appliance, as it only powers the clock.
It can be either a 15 or 20 amp shared circuit.
 

·
" Euro " electrician
Joined
·
5,369 Posts
Minimum 2 small appliance outlets in kitchen. These outlets shall not have any other outlets. (Dedicated)
Just run a dedicated circuit for the countertop microwave.
Personally i would run another dedicated outlet for the range hood. I dont believe it is considered a small appliance.
Although it may not be required, to do it now would save time and money later.

The gas range is not considered a small appliance, as it only powers the clock.
It can be either a 15 or 20 amp shared circuit.

I put a underline part but I just want to double check with ya about the shared circuit which part are you refering to this ??

Merci.
Marc
 
  • Like
Reactions: Thadius856

·
E2 Electrician
Joined
·
5,655 Posts
Read all this twice and not sure I understand fully. I think the concensus is:

Move gas range to one of the small appliance circuits.
Move range hood to lighting circuit.

Now have 3 small appliance circuits, the 3rd one to the single countertop receptacle for the plug in countertop microwave.

If I ever decide to change to micro hood some day down the road, pull 3rd small appliance back up the wall cavity, remove hood from lighting circuit, and drop the spare circuit back down to dedicate to microhood.

Is this correct?
For the most part, or you could new a new 20 amp line now for the hood, it's up to you.
 

·
"So I Re-Wired It"
Joined
·
258 Posts
I put a underline part but I just want to double check with ya about the shared circuit which part are you refering to this ??

Merci.
Marc
I didnt explain well. Was referring to same NEC as Stickboy, adding exception #2.

"Exceptions in 210.52(B)(2) allow clock receptacles and receptacles that are installed to plug in the cords of gas-fired ranges, ovens, or counter-mounted cooking units in order to power up their timers and ignition systems"
 

·
E2 Electrician
Joined
·
5,655 Posts
I didnt explain well. Was referring to same NEC as Stickboy, adding exception #2.

"Exceptions in 210.52(B)(2) allow clock receptacles and receptacles that are installed to plug in the cords of gas-fired ranges, ovens, or counter-mounted cooking units in order to power up their timers and ignition systems"
I knew what you meant. :)
 

·
" Euro " electrician
Joined
·
5,369 Posts
I didnt explain well. Was referring to same NEC as Stickboy, adding exception #2.

"Exceptions in 210.52(B)(2) allow clock receptacles and receptacles that are installed to plug in the cords of gas-fired ranges, ovens, or counter-mounted cooking units in order to power up their timers and ignition systems"
Merci for clearing that one up I almost forgot about the exception #2 but the wiring metholds still the same as far I done for a while.

Side note in France we don't have any exceptions on kitchen circuits on countertop but luminarie ( hardwired ) they do have one for it.

Merci,
Marc
 