Discussion Starter · #1 ·
I finally ordered a ductless mini-split. It needs 220 V AC, and the spec sheet says that a 15 amp fuse is the maximum allowed, with a minimum circuit ampacity of 7.5.

So the cheapest wire I could use is romex 14/2. This is my first time wiring a whole new circuit, and I might want an electrician to be able to inspect it later, so I was thinking I should use MC 12/2 because it's more resilient. Also, if I read the electrical code right, it's an alternative to those fancy AFCI breakers and is actually a lot cheaper. (the AFCI feature makes the same breaker cost $65 more, while wiring with MC raises the cost about 10 bucks)

So I get the wire fished through, and now one end is down in the main panel and the other end is up in the attic. From the example I can see, the A/C disconnect box already installed uses liquid tight flexible non-metallic conduit. I was thinking I would buy a couple of premade pieces of it, and have one piece go from a metal box in the attic, secured to a stud with screws, down the outside wall to the outdoor disconnect. Then from the outdoor disconnect to the mini split. So I terminate the attic wire at a box and use the anti-short bushing and one of those grommets they make for MC.

So far so good. Just one question. What do I do with MC in an electrical panel? I get the MC to the electrical panel, now how do I secure it? All the examples I see are using Romex and in this 2/3 full panel, most of the holes probably already have cables. I know to wear insulated gloves and to turn off the main breaker, and it's a QO load center so there's unfortunately no way to disconnect the main lugs at the top, so I'm thinking I should push the MC in from the back (where there's already a bunch of wiring), about halfway down the panel away from the main lugs. Now the last step is to somehow secure the MC inside the panel with a strap, and I don't know how you're supposed to do that.
 

· Super Moderator
Joined
·
18,305 Posts
First, the 240 volt circuit does not need afci protection. Secondly, if the circuit did require afci protection it does not matter whether you used NM or MC.

The cable connects to the panel with the appropriate connnector. The wires are not secured in the panel.
 

· Registered
Joined
·
6,036 Posts
The metal jacket of the MC does not enter the panel. It goes into a MC connector. Only the wires enter the panel and they are treated just like the other wires in the panel.
If you fished this MC cable into the wall and ceiling, there is no requirement to strap it.

You can mount a box in the ceiling where the MC meets the Flexible plastic conduit with the each getting the correct connector. Then just use wire nuts inside the box and put a blank plate over it. This J-Box must be accessible.
 