Yes and yes
Great thanks. Last question; so if the legend says #6-14, then per NEC you are only allowed one (1) conductor per terminal so either a 6,8, 12, or 14 (co) is allowed in that terminal, yes?That triple tap is not legal and neither is that GEC. The armor should be removed and the cable should be terminated with an approved connector.
That is correct.Great thanks. Last question; so if the legend says #6-14, then per NEC you are only allowed one (1) conductor per terminal so either a 6,8, 12, or 14 (co) is allowed in that terminal, yes?
Been like that for years.Where is the disimmilar metal reaction?Anyone else notice the aluminum and coper wires in direct contact under that clamp?