I recently replaced the receptacle for our washing machine with a GFCI receptacle. This is located in our unfinished basement, near a sink. The old receptacle was rated 15A, so I put in a 15A GFCI (20A pass thru). The receptacle is the only thing on the circuit, the breaker is 20A, and I verified the wiring is 12 AWG.
I know the NEC says that a 15A receptacle is OK on a 20A circuit as long as there are at least two receptacles on the circuit, and since it's a duplex that counts as two.
I don't necessarily want to just meet code, though. I want to make sure it's safe. In our case, the washer is rated 10A, and the iron that we plug into the same receptacle is also rated 10A. So my concern is whether running both the washer and the iron at the same time (total 20A) would exceed the capacity of the 15A receptacle, while at the same time it wouldn't trip the breaker.
I'd appreciate opinions on whether I should replace the 15A GFCI with a 20A, or whether it's fine as it is. Thanks.
I know the NEC says that a 15A receptacle is OK on a 20A circuit as long as there are at least two receptacles on the circuit, and since it's a duplex that counts as two.
I don't necessarily want to just meet code, though. I want to make sure it's safe. In our case, the washer is rated 10A, and the iron that we plug into the same receptacle is also rated 10A. So my concern is whether running both the washer and the iron at the same time (total 20A) would exceed the capacity of the 15A receptacle, while at the same time it wouldn't trip the breaker.