My wife's closet/dressing room has a switch/outlet combination unit on the wall. Today I decided to replace the current unit with a GFCI outlet/switch unit. Upon turning off the power and removing the old switch I became confused. There is only one standard 3 wire romex line running into the box. Looking at the picture of the old switch below, the white wire was connected to the top left terminal, the black wire was connected to the terminal directly below the white one, and the bare wire (ground) was connected to the terminal by itself at the bottom right. I'm really confused what the original electrician did here. I'm also including a picture of the back of the new switch, so if you can provide some suggestions on how to wire it I would be eternally grateful.



 

· Super Moderator
Joined
·
18,333 Posts
I can tell you that the 2 blacks are on the wrong side of the GFI. You have them where the neutral or white should connect. You also have them on the terminals that go to other devices downstream that need GFI protection. Where is the white wire?
 

· Registered
Joined
·
9 Posts
Discussion Starter · #3 ·
I can tell you that the 2 blacks are on the wrong side of the GFI. You have them where the neutral or white should connect. You also have them on the terminals that go to other devices downstream that need GFI protection. Where is the white wire?
I'm confused by what you mean, as I haven't done any wiring yet and just posted pictures of the backs of the two outlets. The top picture is of the old outlet, and the bottom is of the new one. On the new outlet the two permanently connected black wires are for controlling the switch portion of the unit. I just took my little non-contact voltage tester and checked the wires, and it seems as if the white wire is hot in this box. I'm pretty sure the black is supposed to be the hot, so I'm guessing whoever wired this switch originally mixed things up somewhere.
 

· Registered
Joined
·
189 Posts
seannymurrs said:
I'm confused by what you mean, as I haven't done any wiring yet and just posted pictures of the backs of the two outlets. The top picture is of the old outlet, and the bottom is of the new one. On the new outlet the two permanently connected black wires are for controlling the switch portion of the unit. I just took my little non-contact voltage tester and checked the wires, and it seems as if the white wire is hot in this box. I'm pretty sure the black is supposed to be the hot, so I'm guessing whoever wired this switch originally mixed things up somewhere.
Sounds like a switch loop which now violates code to have a nuetral at every switch location which u probably dont, can u take a pic of the switch box itself so we can see the wires
 

· Registered
Joined
·
9 Posts
Discussion Starter · #7 ·
Thats actually two wire romex, three wire eould have black, red, white, ground, anyway do u havd a meter measure white to ground and see wat u get then we'll go from there
I do not have a meter measure. All I have is a non-contact voltage meter. When the power is turned on the white wire sets off the meter and the ground and black do nothing.
 

· A "Handy Husband"
Joined
·
15,062 Posts
The bare ground wire was used as a switched hot leg to the light. Totally non-compliant and dangerous. You should get an electricain in to rewire that circuit properly
 

· Registered
Joined
·
189 Posts
seannymurrs said:
I do not have a meter measure. All I have is a non-contact voltage meter. When the power is turned on the white wire sets off the meter and the ground and black do nothing.
Sounds like a switch loop where the feed enters the light first then comes back to switch, on the previous switch outlet set up did the outlet ever work, bc u dont have a nuetral
 

· Registered
Joined
·
9 Posts
Discussion Starter · #10 ·
Sounds like a switch loop where the feed enters the light first then comes back to switch, on the previous switch outlet set up did the outlet ever work, bc u dont have a nuetral
Yes, the outlet worked fine. Unfortunately a lot of what you're saying is going over my head, as I have very little experience with electrical work.
 

· Registered
Joined
·
189 Posts
seannymurrs said:
Yes, the outlet worked fine. Unfortunately a lot of what you're saying is going over my head, as I have very little experience with electrical work.
Just from u saying that i recommend getting a liscenced electrician, if they are using the bare ground as switch leg u have a dangerous situation, if u set it back up the way it was ur most likely going to dead short against that metal box. So get an ELECTRICIAN asap
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
You say that the bare ground wire was originally connected to the bottom right terminal in your picture. You mean the gold screw, not the green one, right? If so, then they were using the ground wire as the neutral return for the receptacle. The white wire was being used as a switch leg for the light. You cannot install a receptacle in that box without rewiring.
 

· Registered
Joined
·
189 Posts
seannymurrs said:
And just to clarify, putting the old switch back how I found it would be dangerous as well?
Its possible with that bare switch leg or nuetral, without a meter cant tell what, you probably stuff the box while putting it back and that bare wire could come in contact with metal box

Sent from my iPhone using DIY Forum
 

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
And just to clarify, putting the old switch back how I found it would be dangerous as well?
Yes. It was a dangerous installation and far from code compliant. That box was wired for a regular switch, not a switch and receptacle.
 
  • Like
Reactions: NJMarine

· Semi-Pro Electro-Geek
Joined
·
3,404 Posts
Its possible with that bare switch leg or nuetral, without a meter cant tell what, you probably stuff the box while putting it back and that bare wire could come in contact with metal box
The ground was used as the neutral for the receptacle (see his description of the wiring in the original post). The box looks plastic to me.
 

· Electrical Contractor
Joined
·
1,995 Posts
Someone rewired that so they could have a receptacle. If you want to have a receptacle there you will need to fish 12-3 or 14-3 whatever gauge is there currently. Probably easier to have it put back to a switch leg the way it was originally and leave it alone.
 

· Registered
Joined
·
617 Posts
I do not have a meter measure. All I have is a non-contact voltage meter. When the power is turned on the white wire sets off the meter and the ground and black do nothing.
This is why punctuation, spelling and syntax are important, folks. They're not just something your grade school teachers thought of to annoy you.
Thats actually two wire romex, three wire eould have black, red, white, ground, anyway do u havd a meter measure white to ground and see wat u get then we'll go from there
Should have been:
That's actually two wire Romex. "Three wire" would have black, red, white, and ground. Anyway, do you have a meter? Measure white to ground and see what you get. We'll go from there.
 