I'm finishing off my attic and I have a question. Is it generally ok to run Romex in the void of an A-frame attic? I'm planning to insulate the entire thing so there will be fiberglass insulation between all the ceiling joists. I've run a bunch of IC recessed fixtures along the flat part of the ceiling as shown in my quick sketch below. I guess I'm wondering whether I should have used conduit. I have plastic attic vents running from the bottom soffit up to the void created by the ceiling joists and I installed a ridge vent at the top for air flow. I figured since I could run Romex without conduit in my walls, the ceiling should be the same thing right?
 

·
Super Moderator
Joined
·
10,196 Posts
You are fine. Just remember to staple the wire at every 4.5 feet, and where it enters into the light junction box.
 

·
Registered
Joined
·
2,294 Posts
Just remember to staple the wire at every 4.5 feet
That's dumb.

It's code, but it's dumb.

I guess they expect leprecons to get in there some day and pull on the cable :yes:. There is no access to an "attic" like this. It's used for insulation and mechanical systems.
 

·
Super Moderator
Joined
·
10,196 Posts
That's dumb.

It's code, but it's dumb.

I guess they expect leprecons to get in there some day and pull on the cable :yes:. There is no access to an "attic" like this. It's used for insulation and mechanical systems.
We only advocate code correct installations here!:whistling2:
 