4 #10 thwn and 3/4 conduit and a ground rod should set you on the right path.
 

·
Banned
Joined
·
17,248 Posts
Pulling the full 30a 240v @ 100' = 3% voltage drop
Which is acceptable
#10 is actually rated @ 35a...per 310.16....which means you could install a 40a breaker for 35a load & lower
Can't do the 40a breaker....not allowed to upsize the breaker on #10

I think I'd go to #8 & install a 50 breaker
 

·
You talking to me?
Joined
·
7,551 Posts
Pulling the full 30a 240v @ 100' = 3% voltage drop
Which is acceptable
#10 is actually rated @ 35a...per 310.16....which means you could install a 40a breaker for 35a load & lower
I think I'd go to #8 & install a 50 breaker
did you miss that little footnote about #10 Dave? See the asterisk on the wire size on the left and then it refers to 240.4(D)
 

·
You talking to me?
Joined
·
7,551 Posts
in some situations it is allowed but with it would have to fit within one of the exceptions listed in 240.4(D). I may have overlooked it but I found nothing to allow going to the next size breaker for #10 like you would be able to with feeders in general.
 