Is this safe?
EDIT: cant post pics...
EDIT: cant post pics...
Can you explain what you mean by this? It makes no sense.You're very restricted in what you can do with a 30A circuit, since everything is made for 20A maximum, e.g. sockets. So my advice is, don't do it that way.
Personally I'd just run a 20A multi-wire circuit to the shed from the garage panel. That'll give you two 20A circuits to work with, which should be more than enough for a small shed.If I do the modification shown above and feed the shed 120v 30A I will indeed put a sub-panel in the shed with two individual 15A breakers. One breaker will just have two lights on a switch, the other will be a single receptacle.
And my advice is, don't call a receptacle a "socket". While I know you mean "wall socket" (receptacle), others may be wondering about lamp sockets, etc.......since everything is made for 20A maximum, e.g. sockets. So my advice is, don't do it that way.
It's not relevant since he's planning to put in a panel, but I meant that common things that he'd probably want to use like common duplex sockets, GFCI sockets, etc. either aren't available in 30A versions, or would be hard to find.Can you explain what you mean by this? It makes no sense.
Yeah yeah you're right, but receptacle is a mouthful and I spell it wrong every time.And my advice is, don't call a receptacle a "socket". While I know you mean "wall socket" (receptacle), others may be wondering about lamp sockets, etc.
I would if I could. The garage is finished, I don't want to start tearing down drywall just to run some shed lighting. The outside junction box is completely accessible and is ~15 feet from the shed. Pulling 120v 30A from the junction box is the simplest solution.Personally I'd just run a 20A multi-wire circuit to the shed from the garage panel. That'll give you two 20A circuits to work with, which should be more than enough for a small shed.
What 60 amp feed? According to your diagram it's a 30 amp feed. The fact that you have a panel that is rated for 60 amps doesn't change the 30 amp feed.The 240v 60A feed was literally installed just to run the sub-panel (three 120v 15A breakers).
Luke, sorry to sound harsh, but you don't know what you're talking about.It's not relevant since he's planning to put in a panel, but I meant that common things that he'd probably want to use like common duplex sockets, GFCI sockets, etc. either aren't available in 30A versions, or would be hard to find.
Let me try again. You can put a 15A receptacle on a 20A circuit, but it's not legal to put a 15A or 20A receptacle on a 30A circuit. Do you still disagree?Luke, sorry to sound harsh, but you don't know what you're talking about.
"Common" duplex receptacles are either 15 or 20 amp configuration. Same goes for typical GFI receptacles.
That was my assumption, but I've never looked for such a thing. Though of course, you could always use an adapter if you had to.It's not that they are not "available" in 30A versions, it's that 30A is different from 15 or 20A. There is NO such thing as a 30A receptacle that will even accept a 15A plug. It's not that they are "hard to find", it's that they don't exist.
You can put two or more 15A receptacles on a 20A circuit. Neither can be on a 30A circuit.Let me try again. You can put a 15A receptacle on a 20A circuit, but it's not legal to put a 15A or 20A receptacle on a 30A circuit. Do you still disagree?
An adapter would likely not be listed or complaint, other than maybe an adapter for an RV receptacle. You CANNOT have a 15 or 20A receptacles fused or breakered at 30A.That was my assumption, but I've never looked for such a thing. Though of course, you could always use an adapter if you had to.
My mistake. I thought amps were added together how volts are added together. So two 120v 30A lines = 240v 30A, correct?What 60 amp feed? According to your diagram it's a 30 amp feed. The fact that you have a panel that is rated for 60 amps doesn't change the 30 amp feed.
Four? I only need to add three (L1 hot, neutral, ground). There's room for three more wires.What size is that outside junction box ? It might be too small to add 4 more conductors. You need to detireman the cu in capacity and do a fill calc on it.
Could I just swap the 30A two-pole breaker in the house with a 20A two-pole breaker? Bringing the entire circuit down to 20A and eliminating the need for a sub-panel in the shed. The lights and receptacle in the shed would run off of a single 20A circuit.If you do come off of there, you will need a subpanel in the shed so you can mount 15 or 20 amp breakers to reduce the circuit amperage.
I think the 20 amp MWBC off of either of your existing panels is the way to go.
Okay then. That's really all I meant to say originally. Sorry for derailing the thread.You can put two or more 15A receptacles on a 20A circuit. Neither can be on a 30A circuit.
Possibly if it had a a 15A or 20A fuse integrated.An adapter would likely not be listed or complaint, other than maybe an adapter for an RV receptacle.