What’s the best way to protect SER wire?

I have a surface mounted sub-panel and it needs to penetrate the wall and run up to the panel. Can I use EMT conduit for that short run of about 4 feet? Maybe a 2 inch EMT?

It’s a 2-2-2-4 wire so it’s a little less than an inch.
 

·
Registered
Joined
·
34 Posts
Discussion Starter #3
What’s the best way to protect SER wire?
Protected from what?


Can I use EMT conduit for that short run of about 4 feet?
If the install lends itself to mounting conduit... pull THHN
It’s going to be on stucco on the interior or my garage. I feel more comfortable keep that wire protected.

For most of the wire, it’s going to be within the wall and crawl space. It’s only the last 4-5 feet after it transitions to out the wall. Thinking about just using a short 2 inch conduit for a sleeve for that 4 feet.
 

·
A "Handy Husband"
Joined
·
11,845 Posts
Get apiece of 2" schedule 80 PVC conduit. Rip it in half on a table saw and use as a "U" guard over the SER.

Sent from my RCT6213W22 using Tapatalk
 