Proper voltage measuring procedure

2176 Views 13 Replies 8 Participants Last post by  AllanJ
In the past few days there have been two separate threads here which had posts that suggested that measuring voltage between hot and ground (green/bare) either shouldn't be performed at all, or should be performed with one eyebrow raised because the value might need some interpreting.

Now...at the risk of appearing to be an ignorant fool to the amazing professional electrical gods on this site (like Snoopy) who are here to save all of us from impending electrical doom...What have I missed?????
1 - 14 of 14 Posts
If you measure hot to neutral and you read 0V, you need to measure hot to ground to see if you are missing the hot or neutral.
k_buz said:
If you measure hot to neutral and you read 0V, you need to measure hot to ground to see if you are missing the hot or neutral.
EXACTLY!! Which only supports the use of the ground as part of a number of troubleshooting procedures.

I don't get why some say it shouldn't be used.
I don't know what threads you are referring to, so I cannot comment on those specific issues.
As K buz says using the ground can help to identify the problems.

Can you link to the threads in question?
Its done all the time and can't think of a reason not to. You may get a better reading if you meter to ground rather than neutral.
  • Like
Reactions: 1
Its done all the time and can't think of a reason not to. You may get a better reading if you meter to ground rather than neutral.
Yeah...on this website I'll bet the number of posts about 'loose neutrals' outnumbers the posts about loose or false grounds/bonds by 100 fold. My point being, when troubleshooting, a faulty neutral conductor can be just as problematic as a faulty or improperly installed ground/bond conductor, so having both of them at ones' disposal for troubleshooting is quite nice.

What say you, Red Squirrel and AllanJ?? I'm not trying to pick on you...I'm just perplexed by your comments.
It is possible to get into trouble by measuring only hot to ground. It is necessary to always measure hot to neutral, or in the case of a 240 volt circuit, hot to hot, to verify correct operation of the circuit. In the case of three phase power (rare in residential service), it is necessary to measure voltage between the phases, and voltage between phase and neutral. Many three phase services do not have an independent ground, for those services hot to ground has no meaning (in many three phase services, the neutral is grounded, but not always).

A recent near fatal incident at West Valley, NY (a nuclear waste storage site I worked at) shows measurement issues. The electrician was assigned the task of removing a presumably dead three phase service from an abandoned building. He checked phase to neutral for all three phases, and reported zero reading. There was no independent ground on the service. He then attempted to remove a portion of the service. Fortunately he was wearing full arc flash protective equipment, as he dead shorted across two phases, and welded his wrench to the bars, and sustained limited injury (no arc flash gear, he would likely have died). In the accident report, the proximate cause was improper zero energy check. Apparently the electrician never measured phase to phase voltage, and the neutral was disconnected, thus phase to neutral produced no reading.

A somewhat similar incident occurred recently at a nuclear plant in South Carolina. The electrician was assigned the task of removing a defective lug from a three phase service. He followed standard zero energy test procedures, by measuring voltage from phase to phase, and phase to neutral (there was no independent ground). In all cases, the reading was zero. Upon attempting to remove the damaged lug, there was an arc flash, leading to limited injury to the electrician (he had on full protective equipment). The proximate cause of the injury was improper voltage detection procedure. It appears that the particular voltmeter he was using had a button which allowed a remote reading to be captured. This technique had been used previously when measuring voltage in a difficult to access area, and the zero reading had been locked into the machine. Despite the presence of a low tone and a small LED light, the electrician failed to note that the zero readings on the live three phase service represented a locked reading from a previous measurement.

Despite the fact that stringent safety procedures are in place at all nuclear plants I am familiar with, and despite the fact that trained electricians perform all work, serious and even fatal accidents continue to occur at nuclear plants in the performance of routine electrical work. So how does this relate to measurement at home?

I am relatively certain that the average homeowner does not have a written check list procedure for measuring voltage. They probably do not employ exactly the same procedure each time. They probably do not employ stand down procedures if the reading they get is not what was expected. They likely do not use standardized lockout and tag out procedures. They almost certainly do not have arc flash protective equipment. They probably lack professional training. What is amazing to me is not that accidents occur, but that electrical accidents are not more frequent. Possibly this is because the average homeowner is uncomfortable around electricity, and perhaps does not undertake more complex and dangerous tasks such as installing a service, or installing a panel. Plus very few homes have three phase service, and at least in the U.S. voltage is limited to 240 volts in most residential services.

As to the question originally posed, it should certainly be part of every zero energy check to measure leg to leg (240 volt), leg to neutral, and leg to ground. It should also be part of every zero energy check to verify correct operation of the instrument by testing a known source first. I don't know why anyone would suggest that there is a reason not to test leg to ground. It is essential that the individual stop for a minute to consider the results of the zero energy check after performing it. Were the results as expected? If not, DO NOT PROCEED further without a full understanding of exactly what the readings indicate.
See less See more
  • Like
Reactions: 2
I can't speak for the others, but a ground wire is very important in finding loose or missing neutrals or hots.
  • Like
Reactions: 3
Nothing requires a ground wire to work. If you are looking for power at a receptacle for example, you would measure across the hot and the neutral. Using the ground as a reference is only helpful in trouble shooting. If you read 120 volts from hot to ground, that does not mean your appliance will work.
You could remove every single grounding wire in a structure and everything would still work. So why would measuring to ground for any other purpose than to troubleshoot would be a waste of time. Using the ground can also make it much more confusing. Seems DIY'ers have a thing with this bare wire.
The ground wire does nothing but provide a safety feature in your electrical system. It is not required to operate anything.
J. V. said:
Nothing requires a ground wire to work. If you are looking for power at a receptacle for example, you would measure across the hot and the neutral. Using the ground as a reference is only helpful in trouble shooting. If you read 120 volts from hot to ground, that does not mean your appliance will work.
You could remove every single grounding wire in a structure and everything would still work. So why would measuring to ground for any other purpose than to troubleshoot would be a waste of time. Using the ground can also make it much more confusing. Seems DIY'ers have a thing with this bare wire.
The ground wire does nothing but provide a safety feature in your electrical system. It is not required to operate anything.
JV...no disrespect intended...but what in tarnation are you talking about? Troubleshooting was the theme from square-1.
J. V. said:
Nothing requires a ground wire to work. If you are looking for power at a receptacle for example, you would measure across the hot and the neutral. Using the ground as a reference is only helpful in trouble shooting. If you read 120 volts from hot to ground, that does not mean your appliance will work.
You could remove every single grounding wire in a structure and everything would still work. So why would measuring to ground for any other purpose than to troubleshoot would be a waste of time. Using the ground can also make it much more confusing. Seems DIY'ers have a thing with this bare wire.
The ground wire does nothing but provide a safety feature in your electrical system. It is not required to operate anything.
Sorry to disagree but as an HVAC mechanic, all newer furnaces require a ground for the control module to work properly. Some modules even have an LED diagnostics code that tells you the FAU is improperly grounded. Depending on the make and model, the furnace might work but often erratically and will probably lead to early failure of the electronics.
Sorry to disagree but as an HVAC mechanic, all newer furnaces require a ground for the control module to work properly. Some modules even have an LED diagnostics code that tells you the FAU is improperly grounded. Depending on the make and model, the furnace might work but often erratically and will probably lead to early failure of the electronics.
This is to reduce the effects of electromagnetic fields ranging from RFI to that from a nearby blower motor. It's the same problem that leads to hum and noise in audio systems.

But lack of a ground will not affect the voltage of the incoming power supply or the number of available amperes.