Hello. I'm going to run a portable generator somewhere around the 8.5k - 10k size. I plan to use a Square D Interlock kit to back feed the panel legally and safely. What is an appropriate size of inlet box to get and what is the appropriate size of feed breaker to get for the generator sizing above?

Also, if you recommend a size and can tell me the range it would be best for (for example a generator up to 15k should I go that route) I'd appreciate it!

It seems all the inlet boxes I see are 30AMP boxes ... Do they sell larger, should I need it?

ANY AND ALL SUGGESTIONS AND RECOMMENDATIONS ARE APPRECIATED!
 

·
Registered
Joined
·
6 Posts
Discussion Starter · #5 ·
I see. My original question was what is the appropriate size for an 8.5k to 10k generator? I may be completley fine with a 30AMP. Looking for thoughts around proper sizing and the correct sizing of the backfed breaker?
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
I see. My original question was what is the appropriate size for an 8.5k to 10k generator? I may be completley fine with a 30AMP. Looking for thoughts around proper sizing and the correct sizing of the backfed breaker?
Use whatever the largest size receptacle is on the generator you get. 20, 30 or 50.
 