Discussion Starter · #1 ·
Could somebody please tell me if I could use 12/3 AWG to wire my old lincoln welder?

I ran a 12 space QO load center for a sub panel from my house to my garage approx 25ft from each end of the wire, with 3, 4 AWG thhn wires on a 60 amp circuit.

The 4 AWG wires are housed in 1" schedule 40 rigid PVC conduit from panel to panel.

The welder is a lincoln AC-225-S "buzz box". It is on a 30 amp dedicated circuit.

I had the welder wired temporarily wired using some of the left over #4 AWG untill I was ready to set my garage up permanently, and hope I can just use the 12/3
because the #4 AWG is a bear to work with?

Also did I do everything else right so that if I ever sell my house it wont raise any questions as to how the wiring was done? I know you dont know my local codes but according to the NEC?

Thanks
Mark
 

· Registered
Joined
·
42 Posts
I think you should have 4 #4 wires between the main and the sub (2 hots, 1 neutral, 1 ground). The ground and the neutral should be on separate busbars in the sub and neutral busbar should not be bonded. You will need to use #10 for a 30 amp breaker, #8 for a 40, and #6 for a 50. What size breaker you need is dependent on the welder, and I know absolutely nothing about welders.
 

· Registered
Joined
·
46 Posts
Discussion Starter · #6 ·
Ok here is the requirements for the welder
INPUT
-Single phase
-60hertz
-230v
-50 amps
OUTPUT
-225 amps max at 25 arc volts
-Temperature rise 115 deg c max
-79 volts max ocv at rated input
-20% duty cycle

I have a 8 space sub up right now and want to install the 12 space 24 circuit, main lug, 125 amp box.
The one that is up which I purchased new only has 3 lugs and the neutral bar there is no other ground bar, the bonding screw is not installed, I dont think I could fit another legnth of #4 wire in the 1" schedual 40,it was fun getting the 3 in there. I guess I dont know as much as I thought because my house box has the bare copper ground and neutral wires mixed on the same bus bars?? which I didnt install!! lol now im getting confused lol.
so as it is right now the sub panel is not grounded right? so I will need probable 1 1/2" schedual 40 to run 4 #4 wires right and dig up the 1" that I have now. so how dangerous is the setup that I have right now? should I run the new wires before adding anything else to it? and I should be fine after the main wiring situation is taken care of with the 40 amp breaker or do I need to run the 50 amp breaker for the welder?

Thanks
Mark
if you want I can snap a pic of the boxes???
 

· Registered
Joined
·
46 Posts
Discussion Starter · #7 ·
also the new box is a flush mount so I assume the 36" clearance on front and sides just applies to just you standein infront of it and having room on both sides and in front of you as if you were working on the box? so I guess I will have to move my box or air compressor lol?
 

· Banned
Joined
·
17,249 Posts
Main panel has neutral & grounds mixed
Sub-panels DO NOT & MUST have the 4 wire config to meet code
For a ground it does not have to be #4, not sure what size you need
You will need to add another wire & another bus
Is it a detached garage?
Then you need grounding rods also
I always oversize my conduit - cheap & much easier to pull
I used 1.5" conduit for a 60a subpanel #6 run

#4 may have been overkill for a 60a panel
But since you have the welder maybe not

If the faceplate indicates 50a on the welder then I think you will need that. Unless welders are different - never hooked one up

Is the THHN wire also rated THWN for a buried installation?
That is also required by code
 

· Registered
Joined
·
46 Posts
Discussion Starter · #11 ·
Scuba_Dave : yes # 4 was over kill at the time but I used it in case of future expansins like the welder.
So I should scrap everything and go with at least 1.5" maybe even 2" conduit, keep the #4 wire and add another #4 and ground bus bar which would simply screw to the back of the box right?
Also it is a detached garage so I need to add I think I read somewhere atleast 2 grounding rods?

does the 4th wire, the ground need to be #4 wire? if not this could be easier than what Im thinking it is going to be!
Thanks
Mark
 

· Registered
Joined
·
46 Posts
Discussion Starter · #16 ·
I just want it to be right and safe even if I can get away with it... I think I can get the #10 ground through the 1" fairly easily so that problem is I guess solved! just get another ground bar ,split the neutral and ground wires, use #6 wire to install the welder on a 50 breaker and run the grounding rod(s)! 1 or 2 of them?
I think I need to add up all my stuff in the garage to see what im pulling through my sub panel! so how do I figure that out? I cant remember!
Thanks
Mark
 

· Registered
Joined
·
10 Posts
You should have a 50 amp plug on your welder if not purchase one and install it. also get 50 amp recpt to go with it and
size your wire to the recpt. for 50 amps.
What is the capacity of your main house panel?
Do you have any plumbing in the detached garaged?
 

· Registered
Joined
·
46 Posts
Discussion Starter · #20 ·
money-pit, I have the 50amp receptical and the plug that came on the welder,I am going to buy a 50 amp breaker and as Surrogate said #6 wire for the welder circuit,and a grounding bar.I also need 2 grounding rods(they can go through the wall into the sub ground bar right?) And as long as I can get the #10 wire through the conduit for my ground (which can go to any of the bars in the main box right?) Ill be good. and to make my simple situation complicated what does the NEC say about how many wires I can put in the 1" conduit?

the house I believe is a 200 amp service and there is no plumbing in my garage.

Thanks
Mark
 