I have a house that was built in the 50s. It came with mostly two prong outlets. About half of these outlets tested positive for being grounded and have bare ground wires in them. When updating the outlets to a standard three prong outlet and attaching the bare ground wires to the green ground screw I am now getting “open ground” on the tester. I have retightened the ground wires and am at a loss what what to do. Due to the current COVID orders in my state I won’t be able to get an electrician to evaluate the wiring for a few weeks. So what do I do?
 

· retired framer
Joined
·
72,348 Posts
I have a house that was built in the 50s. It came with mostly two prong outlets. About half of these outlets tested positive for being grounded and have bare ground wires in them. When updating the outlets to a standard three prong outlet and attaching the bare ground wires to the green ground screw I am now getting “open ground” on the tester. I have retightened the ground wires and am at a loss what what to do. Due to the current COVID orders in my state I won’t be able to get an electrician to evaluate the wiring for a few weeks. So what do I do?
So some one added wiring or repaired wiring and used a newer cable but it still isn't grounded.

There is a fix that allows you to use the 3 prong outlets but you have to find the first outlet in the circuit and install a gfce outlet, That will work with out a ground. Then there are label s that go on all the other outlets that say no ground. But they are safe.



 

· Registered
Joined
·
8,239 Posts
Older house. Imagine someone wired from Panel to A to B to C with un-grounded wire (2-wire).

Later, someone wired from C to D with grounded cable.

When you go to change your sockets in C and D, what do you see? A ground wire. So you hook it up and expect everything to be golden. It's not. That ground goes nowhere useful.

In fact, the ground is worse than useless. If an appliance at D has a ground fault, that will cause the appliance to be energized at line voltage. And its ground will carry it to socket D. And guess what. That carries it to socket C, and every appliance plugged into socket C. Now, all of them are energized at line voltage, the grounds are shocking you! This is the danger of an "island of grounds". The ground is a liability unless it goes all the way back to the panel.

---

Fortunately it is legal to retrofit grounds as of NEC 2014. You need to run an appropriate sized ground wire either back to the panel, to metal conduit which goes back to the panel, to any other grounded junction box with large enough ground wire back to the panel, or to the copper ground wires from the panel to ground rods/water pipe etc.

---

If you cannot confirm ground at the outlet, you need to protect the outlet with GFCI, and then apply the sticker "NO EQUIPMENT GROUND" which comes with the GFCI.

Note that a GFCI's "Line" screws accept 2 wires each. Very important. Also note the GFCI has a warning sticker covering something up, which says "Do Not Use. For Wizards Only." or words to that effect. This is for the LOAD feature, which allows that GFCI recep to protect other points-of-use downline. This should never be used! Unless you know exactly what you will be protecting, and doing so makes sense.
 