Joined
·
5 Posts
Discussion Starter · #1 ·
I have replaced a GFI plug. It is about four feet from my fuse box and everytime I hook up the ground wire on the line from the fuse box to the plug it trips. Does this mean there is a short in the ground wire between the plug and fuse box? I have tried three different plugs and same problem each time.
 

· Registered
Joined
·
1,125 Posts
Puzzled by GFCI outlet trip

The ground wire should have no effect on the gfci.

You need to explain more and make sure you use the proper terminology.

The ground wire is bare or green and atteched to the metal frame of the recep.
...Unless there is a Grounded NEUTRAL on that circuit. But then again, he would have the same result when hooking up the Real NEUTRAL wire. (confused:yes::no:) :drink:Don't Drink and Drive!!!
 

· Registered
Joined
·
5 Posts
Discussion Starter · #4 ·
Sorry, I'm not an electrican so I don't know all the correct terminology. When I hook the hot and neutral to the plug without the ground wire it works fine, when I hook the ground up and flip the breaker back on it will trip the GFI after about 2 seconds. Remove the ground wire and it will work fine again. This is the ground wire on the wire that runs from the breaker to the GFI plug, hooking up the wire that runs from there to the bathroom plug has no effect on it. Hope this makes sense to you.
 

· Registered
Joined
·
2,294 Posts
You have some improper wiring going on between the panel and the GFCI.

A properly connected ground will not in any way affect the GFCI.

Somebody must have done something stupid somewhere.:jester:


If you want someone to think the circuit thru we need to know details.

OK.......Again with the guessing games :jester:

At the jbox in question:

Cable comes from panel directly to GFCI ?

Another cable goes out to bathroom receptacles?


.
 

· Registered
Joined
·
5 Posts
Discussion Starter · #6 ·
You have some improper wiring going on between the panel and the GFCI.

A properly connected ground will not in any way affect the GFCI.

Somebody must have done something stupid somewhere.:jester:


If you want someone to think the circuit thru we need to know details.

OK.......Again with the guessing games :jester:

At the jbox in question:

Cable comes from panel directly to GFCI ?
Another cable goes out to bathroom receptacles?


.
yes the cable comes from panel directly to GFCI
yes another cable goes out to bathroom receptacles, one in each bathroom
 

· Registered
Joined
·
117 Posts
We had a problem like this when we were doing a bathroom remodel. Turns out there were 3 rooms on the same circuit including the bathroom. There was a cross somewhere. Didn't feel like finding it so we ran all brand new feeds to each room and put them on there own seperate circuit. The way it is supposed to be. Based off of what i got from what he is saying is that the wire goes from the panel to the gfci. then from there to a bathroom receptical. Something is messed up somewhere. I wonder if he tied the grounds together? How are you wiring the gfci? Are you going line in and line out? so that when the gfci trips everything else stays on? Or line in and load out so that when it trips nothing past the gfci will work?
 

· UAW SKILLED TRADES
Joined
·
4,975 Posts
I don't see how it can be between the breaker and the gfci receptacle since the gfci cannot 'see' that current on that part of the branch circuit. But I agree more details would help.

My questions...

Are you trying to gfci protect your bathroom receptacle/s that were never protected?

If so do you have the cable/wire that goes to the bathrooms connected to the load terminals of the gfci?

Is this gfci in a metal electrical box ?
 

· UAW SKILLED TRADES
Joined
·
4,975 Posts
I forgot one question....do you have something plugged in and turned on at one of the bathroom receptacles or any lights on the same branch circuit turned on in those bathrooms when you turn that breaker back on?
 

· UAW SKILLED TRADES
Joined
·
4,975 Posts
Is the ground wire from the bathroom/s connected when you connect the ground wire from the breaker panel?

Answer the last two questions and I'll tell you what I think your problem is.....
 

· UAW SKILLED TRADES
Joined
·
4,975 Posts
It's late so I'm just going to tell you what I think is going on based on your description.

First you say you are replacing a gfci. That tells me that you thought you had a bad gfci but the new one has not corrected the problem. You also say that the gfci works fine until you connect the bare ground wire in the cable coming from the breaker panel about four feet away.

Only possibility that could cause the gfci to trip is current is leaking to ground on the load side (bathroom cable). When you connect that ground you are completing the circuit for the fault and the gfci is detecting the current loss to ground and trips out. This is because the bathroom cable is connected to the load terminals of the gfci and it senses all current flow irregularities on that cable to the bathrooms.

You also say that there are no lights or other loads operating on the load side of the gfci. So the only way there is any current flow that the gfci can see is if you have a fault to ground with the hot wire some where on the cable going to the bathrooms.

If the box the gfci is in is metal you could have a fault to the metal so be careful. Usually this is a result of a metal clamp being tightened too much on the cable to the bathroom piercing the insulation of the cable and hot wire and just barely making contact with the metal of the box completing a circuit over the ground that allows only a very small amount of current to flow on the hot wire and the gfci trips because it is detecting zero current flow in the neutral of the cable to the bathroom.

That's one possibility.

The second is the fault exists on a hot to ground somewhere else on the branch circuit. To test this disconnect the ground on the bathroom cable and keep it from touching anything especially the metal of the box if it's metal. Connect the ground from the breaker panel as you have been doing along with all the hots and neutrals to the gfci. Turn the power on. If the gfci trips then you know the fault exists at the box the gfci is in. If it holds then you know that unwanted current is on the ground in the cable to the bathrooms and you will have to investigate all switch boxes and receptacle boxes and fixture boxes to find the fault.

Another thing to consider is if any one has been driving any nails or screws into the walls piercing that bathroom cable.
 

· Registered
Joined
·
1,125 Posts
Puzzled as to why GFCI recept. trips whn. gnd. hk. up

I forgot one question....do you have something plugged in and turned on at one of the bathroom receptacles or any lights on the same branch circuit turned on in those bathrooms when you turn that breaker back on?
...But then the GFCI Would trip when the NEUTRAL is hooked up, which would make sense. But jbf... claims that when Neutral is hooked up nothin' happens. Only when the GROUND wire is hooked up is when the Recept. trips out. There's some information missing here or Terminology not properly applied. I'm willing to bet that there's a GROUNDED NEUTRAL somewhere! (No matter What):yes::no::drink:Don't drink and Drive!!!
 

· UAW SKILLED TRADES
Joined
·
4,975 Posts
Yes thats a possibility but a grounded neutral must have current flow. Without a load operating there will be no current flow on the neutral unless it is faulted to a hot wire. If the neutral was faulted to ground nothing would happen at the gfci when power was restored because there is no current flow till a load operates. If the gfci was tripping when he turned on a load I would say you are correct but it trips only when that ground is connected and under no load on the branch circuit. So what I'm saying is without load on the branch circuit the hot wire has to be faulted. It may be that the neutral and ground and hot are all involved. But the breaker is holding so whatever the hot is faulted to is very suttle.
 

· Registered
Joined
·
2,294 Posts
I hate speculating with soooo many questions.:yes:

It's going to one of those "that would have been nice to know" things :yes:

I still don't know if it's a fuse or a breaker.:laughing:

I do know that:

A) It's not a newer/stock installation because the HR would go directly to bathroom #1 first.

B) A neutral to ground short on the line side wouldn't affect it.

When you get back to it, check the line VS load wiring.

Line = power in, load = power out
 

· Registered
Joined
·
1,125 Posts
Speculating (to the nTH degree)

Yes thats a possibility but a grounded neutral must have current flow. Without a load operating there will be no current flow on the neutral unless it is faulted to a hot wire. If the neutral was faulted to ground nothing would happen at the gfci when power was restored because there is no current flow till a load operates. If the gfci was tripping when he turned on a load I would say you are correct but it trips only when that ground is connected and under no load on the branch circuit. So what I'm saying is without load on the branch circuit the hot wire has to be faulted. It may be that the neutral and ground and hot are all involved. But the breaker is holding so whatever the hot is faulted to is very suttle.
At this point, we're all speculating to the n-th. Degree. We might as well be on Wall Street. Certainly, there is incomplete information here. Most likely, the branch circuit extends beyond the bathroom receptacle. Assuming that is the case, there might be a load albeit a small one somewhere along the line. On a more practical level, jdf... needs to do some Continuity testing on all parts of the circuit. That'll reveal where the unwanted conductivity is! (No Matter What):yes::no::drink:Don't Drink and Drive!!!
 

· UAW SKILLED TRADES
Joined
·
4,975 Posts
Not likely... the OP replaced one he thought was bad and the new one is also tripping out....at least that is how it appears on the surface.


As 220/221 and spark plug have said more details will help but I don't think we are speculating that much if the results given by the OP are correct.
 